Yes, this is possible. One would need to design a new Real-Time viewing table file (ex. Harmonics.PML) which would address the appropriate available Modbus registers.
I would suggest opening one of the existing PML files available in the folder which the device is using (see Device Properties -> Display and go to the C:\Program Files (x86)\Schneider Electric\ION Setup\Tables\PM5000 folder and move into the highlighted folder).
You will need to first use Explorer to copy one of the files and rename it. Then use Notepad (Run as Administrator) to edit the labels and register references in the file.
Link copied. Please paste this link to share this article on your social media post.
Yes, this is possible. One would need to design a new Real-Time viewing table file (ex. Harmonics.PML) which would address the appropriate available Modbus registers.
I would suggest opening one of the existing PML files available in the folder which the device is using (see Device Properties -> Display and go to the C:\Program Files (x86)\Schneider Electric\ION Setup\Tables\PM5000 folder and move into the highlighted folder).
You will need to first use Explorer to copy one of the files and rename it. Then use Notepad (Run as Administrator) to edit the labels and register references in the file.