Calculating Logging Storage Length in the PM5560 Datalog 1

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

JamesAZZO
Sisko | EcoXpert Master Sisko | EcoXpert Master
Sisko | EcoXpert Master
0 Likes
9
697

Calculating Logging Storage Length in the PM5560 Datalog 1

Is there a simple formula for calculating how many days of logging is available in Datalog #1 when configured at 5 minute intervals and all 16 channels of logs are used?

9 Replies 9
sesa54412_bridg
Crewman Crewman
Crewman
0 Likes
8
549

Re: Calculating Logging Storage Length in the PM5560 Datalog 1

Hi James,

The maximum log size for the PM556x (PM5560, PM5561 and PM5563) is 35040 records total.

In your scenario: the number of records, N=16 and the logging frequency: f = 5min intervals or 12 readings/hour

The number of records per day is R = N*f*24 = 16*12*24 = 4608 records/day

The total number of days, with this scenario, is 35040/R = 35040/4608 = 7.6 days or 7d 14h 30m


If you are logging at this rate, I would suggest having some supervisory system (like StruxureWare PowerSCADA Expert or StruxureWare Power Monitoring Expert) to poll the meter to ensure a contiguous database.


If I can ask, What scenario or system are you configuring the PM556x (in this way) for ?


Kind Regards,

Chris.

JamesAZZO
Sisko | EcoXpert Master Sisko | EcoXpert Master
Sisko | EcoXpert Master
0 Likes
7
549

Re: Calculating Logging Storage Length in the PM5560 Datalog 1

We will have PME, but requirements are 2 weeks onboard logging as it's a remote site and connection by 3G isn't always reliable there.

5 min logs is because of solar sources being measured. Cloud cover changing makes fast changes we want to see over 5 minutes.

sesa54412_bridg
Crewman Crewman
Crewman
0 Likes
6
549

Re: Calculating Logging Storage Length in the PM5560 Datalog 1

Hi James,

What are the 16 parameters you are wanting to record at this rate ?  Can you share how you might prioritize them ?

Best Regards,

Chris.

JamesAZZO
Sisko | EcoXpert Master Sisko | EcoXpert Master
Sisko | EcoXpert Master

Re: Calculating Logging Storage Length in the PM5560 Datalog 1

  1. Real Energy Into the Lord
  2. Real Energy Out of the Load
  3. Demand Real Power Total
  4. Real Power Total
  5. Real Power A
  6. Real Power B
  7. Real Power C
  8. Reactive Power Total
  9. Apparent Power Total
  10. Power Factor Sign Total
  11. Vln avg
  12. Vln avg
  13. I avg
  14. THD V1
  15. THD V2
  16. THD V3
Daniel_Brandao
Lt. Commander Lt. Commander
Lt. Commander

Re: Re: Calculating Logging Storage Length in the PM5560 Datalog 1

James, the maximum number of values you can record is 14, not 16. We are working on a spreadsheet that will automatically calculate how many days of logs you will have, based on the parameters you select and the frequency of logging. I will send you a draft version and we will publish after it's validated.

And you should be able to log 14 values every 5 minutes for around 50 days.

Let me know if questions.

michaelthode
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
1
549

Re: Calculating Logging Storage Length in the PM5560 Datalog 1

Is it well understood that there can be saved over 200.000 logs in PM5561?
If the formula in the first answer is right, the capacity will be 201.600?

the leaflet says: 6 parameters for 90 days with 15 munutters interval.

Can you help find the accurate logging calculation? 🙂

Best regards

Michael Thode

dborle
Lt. Commander
Lt. Commander
0 Likes
0
549

Re: Calculating Logging Storage Length in the PM5560 Datalog 1

There has been a similar thread [DEAD LINK /message/16555#16555]https://powersolutionscommunity.schneider-electric.com/message/16555#16555. When I use the datalog calculator (spreadsheet from Daniel) I get 55 days for 14 parameters with 5 minutes interval

Regards

Daniel

camilo_gonzalez
Ensign
Ensign
0 Likes
0
549

Re: Calculating Logging Storage Length in the PM5560 Datalog 1

James, is possible Log THD Data?

Im trying with ION Setup but dont appear this parameter.

Regards!

gaamaya_ingea-h
Ensign
Ensign
0 Likes
0
549

Re: Calculating Logging Storage Length in the PM5560 Datalog 1

Daniel Brandao

This could be a very valuable spreadsheet for me. Its been a couple of year since you posted this, so I may guess the spreadsheet is done? haha.. Talking seriously, can someone give me a link to download the spreadsheet? Where can i find it? Since it is not in this thread.

Thanks!