Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

CONECTION PM8000 - PLC WITH MODBUS TCP/IP

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Re: CONECTION PM8000 - PLC WITH MODBUS TCP/IP
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
571
Mehran_Mehrnia
Mehran_Mehrnia Champion
202
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Chriskero
Chriskero
Explorer

Posted: ‎2024-07-01 06:45 AM

0 Likes
1
1807
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-01 06:45 AM

CONECTION PM8000 - PLC WITH MODBUS TCP/IP

 

Good,

I am looking to read various values of power, voltage and current from the PM8000 using the modbus tcp IP protocol, it turns out that the registers are according to the MODBUS mapping of the PM8000 in the addresses 3000-3150, the problem starts when these values are values of type FLOAT and reading registers in the addresses 3000-3150 are bit type and not word.
What solution can I give to be able to read correctly those values?
I would like to communicate with a Siemens PLC.

Thank you very much

 

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2024-07-02 02:12 PM

1 Like
0
1770
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-02 02:12 PM

Hi @Chriskero 

All Float32 registers(Single-precision floating-point format) in PM8000 Modbus map, are two 16-bit registers(two words) in big endian format(the most significant word is stored at the lowest memory address) that need to be swapped:

Mehran_Mehrnia_0-1719953721468.png

Mehran_Mehrnia_1-1719954629830.png


For any queries regarding Metering & Power Quality, kindly post your questions in the following forum link:
https://community.se.com/t5/Metering-Power-Quality/bd-p/power-metering

Thank you.

Best regards,

-Mehran
L3 Expert Tech Support Specialist

See Answer In Context

Reply
Reply 1
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2024-07-02 02:12 PM

1 Like
0
1771
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-02 02:12 PM

Hi @Chriskero 

All Float32 registers(Single-precision floating-point format) in PM8000 Modbus map, are two 16-bit registers(two words) in big endian format(the most significant word is stored at the lowest memory address) that need to be swapped:

Mehran_Mehrnia_0-1719953721468.png

Mehran_Mehrnia_1-1719954629830.png


For any queries regarding Metering & Power Quality, kindly post your questions in the following forum link:
https://community.se.com/t5/Metering-Power-Quality/bd-p/power-metering

Thank you.

Best regards,

-Mehran
L3 Expert Tech Support Specialist

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore