Built in battery backup for in-built real time clock

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
swil
Commander
Commander
0 Likes
5
539

Built in battery backup for in-built real time clock

Q: Is a built in battery back up for the in-built real time clock a standard feature of Schneider Power meters these days?

 

I seem to recall that there is a battery back up for an iEM meter previously encountered.

 

This question is specifically with reference to:
1. PM5350

2. PM5560

 

If it can be answered more generally then that would also be good.

 

Thank you.


Accepted Solutions
Ramasamy_N
Commander Commander
Commander

Re: Built in battery backup for in-built real time clock

Hi @swil 

 

Yes, PM5560 has the inbuilt battery for the real time clock back up. The battery can back up the RTC more than 3 years when the meter stored without control power. 

 

PM5350 has the capacitor to backup the RTC only for 30 seconds, it does not have the inbuilt battery. The updated reference PM5350P has the inbuilt battery for RTC backup. 

 

FYI, iEM3000 series has the super capacitor for the RTC backup, not the battery. 

 

Regards, 

Ramasamy N

See Answer In Context

Ramasamy_N
Commander Commander
Commander

Re: Built in battery backup for in-built real time clock

Yes, PM8000 series has inbuilt battery for RTC backup and the back time will be more than 7 years under specified storage condition. 

 

Regards, 

Ramasamy N

See Answer In Context

5 Replies 5
Ramasamy_N
Commander Commander
Commander

Re: Built in battery backup for in-built real time clock

Hi @swil 

 

Yes, PM5560 has the inbuilt battery for the real time clock back up. The battery can back up the RTC more than 3 years when the meter stored without control power. 

 

PM5350 has the capacitor to backup the RTC only for 30 seconds, it does not have the inbuilt battery. The updated reference PM5350P has the inbuilt battery for RTC backup. 

 

FYI, iEM3000 series has the super capacitor for the RTC backup, not the battery. 

 

Regards, 

Ramasamy N

swil
Commander
Commander
0 Likes
3
532

Re: Built in battery backup for in-built real time clock

Maybe the PM5350P isn't available in Australia.  The only part number available is METSEPM5350

 

Does the PM8000 also have the battery back up for the RTC?

 

Thank you very much.

Tags (1)
Ramasamy_N
Commander Commander
Commander

Re: Built in battery backup for in-built real time clock

Yes, PM8000 series has inbuilt battery for RTC backup and the back time will be more than 7 years under specified storage condition. 

 

Regards, 

Ramasamy N

swil
Commander
Commander
0 Likes
0
524

Re: Built in battery backup for in-built real time clock

Thank you Ramasamy N.

DanL
Commander Commander
Commander

Re: Built in battery backup for in-built real time clock

The PM8000, ION7400, and ION9000 also have provision for a replaceable battery in addition to the built-in 7yrs+ battery.

The part number for the battery replacement kit is METSEPMBATK.