Continue
  • My Subscriptions
  • Events
Positive and Negative Power on PM2000 meters
Metering & Power Quality
  • EcoStruxure Power & Grid
  • Positive and Negative Power on PM2000 meters
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
james-wood-tel
james-wood-tel Explorer
Explorer
Posted: ‎2020-03-09 04:09 AM . Last Modified: ‎2020-03-09 04:24 AM
3879
Hi, Can anyone explain why we are getting the Power Tot jumping between positive to a negative value. Meters used are PM2000 so cannot see how it could be wired incorrectly.
We are getting accumulated energy delivered and received even though there is no energy generation.
Ramasamy_N
Ramasamy_N Champion
Champion
Posted: ‎2020-04-28 11:17 PM
Hi @james,
The PM2200R references must follow the LVCT setup (CT placement and phase sequence)  as specified in the user manual. This seems to be the mismatch of CT placement and sensor selection i
Please check the CT input sequence in the panel and configured sensor type in meter setup page.
Ramasamy N
Replies 5
Charles_Murison
Champion
Posted: ‎2020-03-09 08:40 AM
Hello @james-wood-tel ,
I am not a PM2000 expert but with meters I work with the first question I would have is what is the CT ratio? The PM2000 has measurement range of 5 mA to 6 A, Another question I would have is what is the ratings of the CTs, on many CTs, there is a minimum current required before the becomes accurate. On many CT's this is around 10% of primary rating. For example a 500:5 CT may need 50 amps on primary side (500mA secondary) before accurate which is much higher than the minimum current required for the meter.
Charles
Yut
Yut
Leader
Posted: ‎2020-03-18 02:15 AM
Is there any capacitor bank connected ?
Charles_Murison
Champion
Posted: ‎2020-03-23 11:43 AM
3853
Did you ever get a chance to look into the CT ratio? CT Primary and CT secondary information.
Charles
sesa208600_brid
sesa208600_brid Explorer
Explorer
Posted: ‎2020-03-27 02:43 AM
Hi James,
Can you check the kW per each phase, are these all displaying negative kW or is it just on a specific phase?
zoltan
Ramasamy_N
Ramasamy_N Champion
Champion
Hi @james,
Ramasamy N
