Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Alarm Settings

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Alarm Settings
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Sven_Ortmann
Sven_Ortmann Leader
Leader

Posted: ‎2015-03-11 06:47 AM . Last Modified: ‎2020-04-22 01:45 AM

0 Likes
6
3684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-03-11 06:47 AM

Alarm Settings

Hello,

 

I am trying to setup some Alarms with PM850 device. For me it is not clear how to define the Setpoint Pickup and Dropout in ION Setup.

5901

What are common settings for Europe? And how long should be the Delay? (fastest =0 ?)

 

should this be set on base of Min/Max values?

5902

5903

1) i want a notification if current voltage is +-10% and stop if the current voltage is +-8%

2) i want a notification if the voltage changes +-5% from the nominal voltage.

3) notification if the sinus changes?

 

is this possible?

 

thank you

Labels
  • Labels:
  • ION Setup
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mitun_Paul
Mitun_Paul Troubleshooter
Troubleshooter

Posted: ‎2015-03-12 02:59 AM

2 Likes
0
3545
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-03-12 02:59 AM

To implement this, 4 alarm settings are required.

1. Over Current

2. Over Voltage

3. Under Current

4. Under Voltage

If required you may create separate alarms for each phase.

Setpoint Pickup is the alarm trigger point and at Setpoint Dropout the alarm gets turned off. Please see below example for over and under current setting. Select "Relative (% of Avg) to use % value of nominal voltage of current as a trigger point.

Select the priority as per your requirement. It is required to set some Delay. 0 delay indicates that the alarm is inactive and it will not give any notification, so make sure to enter some value in delay. 1 sec delay is the fastest.

As per the below example,

1. The over current alarm will trigger if the current raises over 110% of the nominal current and stay over 110% for at least 1 sec and it will be turned off if the nominal current fall below 108% and hold it below 108% for more than 1 sec.

2. The under current alarm will trigger if the current drop below 90% of the nominal current and stay below 90% for at least 1 sec and it will be turned off if the nominal current raises over 92% and hold it over 92% for more than 1 sec.

Similarly you may create alarm for over and under voltage also.

5913  5914

See Answer In Context

Reply
Replies 6
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2015-03-11 09:44 AM

0 Likes
1
3545
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-03-11 09:44 AM

Hi Sven,

I'm not an expert on the PM850, but the ION Setup alarm setup is designed to mimic what was available by the older PMCU/SMS configuration software so the UI is mostly similar.

I think you should refer to the PM850 manual but my best guess here is that you'll want to check the "Relative (% of Avg)" checkbox and then enter the values of 110 for Pickup and 108 for the Dropout.  Delays would be how long (in seconds) you want to be above the 10% and below the 8% to consider the alarm to go ON (or OFF).  You would do this for all the current alarms and then similarly make changes for the voltage ones (it sounds like you need to create additional Under current alarms as well (or replace some of the existing ones if you've run out of available standard alarms).

If you don't check the "Relative (% of Avg)" checkbox, then the Pickup and Dropout values are interpreted as absolute values instead of percentages (i.e. a value of 500 would be 5.00 amps above since its multipled by x 0.01).

Reply
Sven_Ortmann
Sven_Ortmann Leader
Leader

Posted: ‎2015-03-12 12:42 AM

0 Likes
0
3545
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-03-12 12:42 AM

Hello Robert,

thank you. But to my understanding with the PM800 Series User guide.

The PM850 should have 33 standard alarms.

5883

but in ION Setup there are 40 Alarms but every Alarm is disabled.

Reply
Mitun_Paul
Mitun_Paul Troubleshooter
Troubleshooter

Posted: ‎2015-03-12 02:59 AM

2 Likes
0
3545
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-03-12 02:59 AM

To implement this, 4 alarm settings are required.

1. Over Current

2. Over Voltage

3. Under Current

4. Under Voltage

If required you may create separate alarms for each phase.

Setpoint Pickup is the alarm trigger point and at Setpoint Dropout the alarm gets turned off. Please see below example for over and under current setting. Select "Relative (% of Avg) to use % value of nominal voltage of current as a trigger point.

Select the priority as per your requirement. It is required to set some Delay. 0 delay indicates that the alarm is inactive and it will not give any notification, so make sure to enter some value in delay. 1 sec delay is the fastest.

As per the below example,

1. The over current alarm will trigger if the current raises over 110% of the nominal current and stay over 110% for at least 1 sec and it will be turned off if the nominal current fall below 108% and hold it below 108% for more than 1 sec.

2. The under current alarm will trigger if the current drop below 90% of the nominal current and stay below 90% for at least 1 sec and it will be turned off if the nominal current raises over 92% and hold it over 92% for more than 1 sec.

Similarly you may create alarm for over and under voltage also.

5913  5914

Reply
sesa17969
sesa17969 Leader
Leader

Posted: ‎2015-03-13 05:57 AM

1 Like
0
3545
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-03-13 05:57 AM

Hi

The answer of Mituh Paul is correct but not complete.

First remark if you select priority None (0) This alarm will not appear in a list of alarms in your scada.

Priority 1 : on the display of the PM alarm flash up to reset this alarm even if alarm disappear.

Priority 2 and 3  on the display of the PM alarm flash up as soon as alarm desappear flash up stop (This setting is recommanded when your PM is connected to a scada)

Second remark when you select "Relative" if the value of voltage, current increase slowly your average value increase also and the setpoint that you would like to detect is not what you think.
I prefer to use a thrue value. I Europ the standard give nominal value and range. For each customer I calculate the setpoint.

Last remark If you more alarm for example E setpoint for over voltage you can add this new alarm, but the number of alarm is limited in the list.

If the message "is not possible" appear you can delete an alarm that you don't use and create your alarm.


Reply
Anonymous user
Not applicable

Posted: ‎2015-04-07 09:15 AM

0 Likes
1
3545
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-04-07 09:15 AM

Hi every body,

Do you have an example how to configure alarm which trigger when the power factor drop below 80 % ?

Best regards.

Reply
sesa139879_brid
sesa139879_brid Leader
Leader

Posted: ‎2015-04-07 12:52 PM

0 Likes
0
3545
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-04-07 12:52 PM

It depends on the device type you are working with, I would suggest to review the device User Guide, there is usually a section that describes how to configure alarms if the device has on board alarm capabilities, otherwise it is possible to configure PC alarms and there is a good solid example on the PME User Guide Pg 195 Common Virtual Processor applications if there are any further questions please let us know

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore