How to update the firmware on a Smart-UPS connected to EcoStruxure IT

IT Expert via ethernet port

Monitor your APC Smart-UPS in EcoStruxure IT Expert using its ethernet port or a Network Management Card (NMC)

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • IT Expert
  • IT Expert via ethernet port
  • How to update the firmware on a Smart-UPS connected to EcoStruxure IT
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Monitoring APC Smart-UPS in EcoStruxure IT
  • EcoStruxure IT features available for Smart-UPS
  • How to register a Smart-UPS using the EcoStruxure ...
  • Does a Smart-UPS with a SmartConnect ethernet port...
  • How to update the firmware on a Smart-UPS connecte...
  • Can I register my SmartConnect-compatible UPS with...
  • How to delete a Smart-UPS from the SmartConnect po...
  • How to remove a Smart-UPS from EcoStruxure IT
  • Monitoring APC Smart-UPS in EcoStruxure IT
  • EcoStruxure IT features available for Smart-UPS
  • How to register a Smart-UPS using the EcoStruxure ...
  • Does a Smart-UPS with a SmartConnect ethernet port...
  • How to update the firmware on a Smart-UPS connecte...
  • Can I register my SmartConnect-compatible UPS with...
  • How to delete a Smart-UPS from the SmartConnect po...
  • How to remove a Smart-UPS from EcoStruxure IT

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

SmartConnect Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to IT Expert via ethernet port
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2782 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to update the firmware on a Smart-UPS connected to EcoStruxure IT

Picard EcoStruxureIT
‎2020-08-18 02:29 AM

Last Updated: Sisko JLehr Sisko ‎2025-08-20 10:41 AM

Smart-UPS connected to EcoStruxure IT using an NMC

 

If your Smart-UPS is connected to EcoStruxure IT using a Network Management Card and you subscribe to IT Expert, you can update the NMC firmware directly in IT Expert.

Log in to IT Expert and go to Management > Firmware Update. See Firmware update

 

To update the firmware on the Smart-UPS device, use a serial or USB connection and the Smart-UPS Firmware Upgrade Wizard.

 

Smart-UPS connected to EcoStruxure IT using the ethernet port

 

If you registered your Smart-UPS with EcoStruxure IT using its ethernet port, you update the firmware on the device using a serial or USB connection and the Smart-UPS Firmware Ugrade Wizard.

You'll find the latest firmware for your device in the wizard.

See APC FAQ FAQ 279197 

Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

Comments
A360
A360
Cadet
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2025-08-06 09:08 AM

So, you are saying a Smart Connected UPS using the ethernet cable CANNOT be updated through IT Expert, even though it CAN be updated through the Smart Connect portal?  If that is the case, it makes ZERO sense to move it off of the Smart Connect portal!!!!!!!!

0 Likes
dmarchewka
dmarchewka
Cadet
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2025-08-07 08:49 AM

UPS NMC firmware, just to clarify, not the UPS firmware.

0 Likes

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore