EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:12 AM . Last Modified: 2024-04-05 03:04 AM
Hi
We recently implemented the DDF file for Uniflair Leonardo in DCE
It seems to work well 😀
It seems that the same DDF file is NOT working in NetBotz device scan
Question is - How to get the DDF for NetBotz, if we have created this?
Thanks in advance 😀
BR
Mogens
(CID:128067672)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:13 AM . Last Modified: 2024-04-05 03:04 AM
Hi Mogens,
I do not believe that NetBotz DDFs are being created at this time. For that, I'll defer to the DDF team if they're aware of any effort in that area.
I do know that the DCE DDFs are too big for the NetBotz appliances and won't work. I suggest removing that DDF and if you must poll the device with a NetBotz appliance, perhaps using the supplemental OID feature will get you the info you need.
Thanks,
Steve
(CID:128067688)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:12 AM . Last Modified: 2024-04-05 03:04 AM
Hi Mogens,
As you probably already know, the DDFs for DCE and NetBotz are different. However, I don't think we are actively writing any new DDFs for NetBotz any more.
Regards
Someone else might want to elaborate on this also.
(CID:128067684)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:13 AM . Last Modified: 2024-04-05 03:04 AM
Hi Mogens,
I do not believe that NetBotz DDFs are being created at this time. For that, I'll defer to the DDF team if they're aware of any effort in that area.
I do know that the DCE DDFs are too big for the NetBotz appliances and won't work. I suggest removing that DDF and if you must poll the device with a NetBotz appliance, perhaps using the supplemental OID feature will get you the info you need.
Thanks,
Steve
(CID:128067688)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:13 AM . Last Modified: 2024-04-05 03:04 AM
OK, thank you John and Steve!
You confirm my expectation on NetBotz DDF, and probably it is rare that customers request this NetBotz SNMP scan feature for new devices.
BR Mogens
(CID:128747771)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:13 AM . Last Modified: 2024-04-05 03:04 AM
Device support team only develops DDFs for DCE and gateway (StruxureOn). I will share you post/question with my developer contact at Netbotz.
(CID:128747774)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:13 AM . Last Modified: 2023-10-22 03:13 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.