After Upgrading DCE to 7.5.0 the ServerTech PDU show in alarm in DCE

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • After Upgrading DCE to 7.5.0 the ServerTech PDU show in alarm in DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
64
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:12 AM . Last Modified: ‎2024-04-05 03:04 AM

0 Likes
4
557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:12 AM . Last Modified: ‎2024-04-05 03:04 AM

After Upgrading DCE to 7.5.0 the ServerTech PDU show in alarm in DCE

After I upgraded DCE to 7.5.0 all the Servertech PDU are in alarm for "Temp/Humid Sensor Temp_Humid_Sensor_A1: a Not Found condition exists"

 

The DDF file that came with this upgrade is causing this, in fact when I remove the DDF file the alert go away. Is there a way to change the DDF file. I have tried to send this to the DDF team using the Device Support web page, but without any luck

 

 

I am using the old Sentry DDF file but it is not working for all the PDU in my environment.

If someone has the same problem and you got the DDF file modified can you please send it to me.

 

Thanks

(CID:128067315)

Labels
  • Labels:
  • Data Center Expert
  • DDF
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:12 AM . Last Modified: ‎2024-04-05 03:04 AM

0 Likes
0
557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:12 AM . Last Modified: ‎2024-04-05 03:04 AM

Dear Vincenzo Fantino,

I am using the old Sentry DDF file but it is not working for all the PDU in my environment.

I.e., in the previous version of DCE software (prior to upgrade), did you use old Sentry DDF-file? And while you did not have the above problems? I understand you correctly? If this is the case, after upgrading to DCE-7.5.0, the Sentry DDF-file was probably modified.

Therefore, there are two ways to solve your problem. The first is to remove the modified Sentry DDF-file from DCE-7.5.0 and import instead of it your old Sentry DDF-file from the previous version of DCE software.

The second way is, if possible, to disable the alarms on the Device Alarms tab for this ServerTech PDU such as "...a Not Found condition exist".

There is a third way - it is the most correct one. For example, simply searching by the keyword tech and by the type of PDU device leads to this result on Device Support:

That is, at least we have three records for this vendor and its PDUs, which are supported by DCE software. Probably you need to try all of them and maybe some of these DDF-files will work fine with your PDUs and with the new version of DCE-7.5.0.

I hope this helps you.

If there are more questions, please ask 😀.

With respect.

(CID:128067333)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:12 AM . Last Modified: ‎2024-04-05 03:04 AM

0 Likes
0
557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:12 AM . Last Modified: ‎2024-04-05 03:04 AM

Dear Vincenzo Fantino,

Have you been able to solve your problem or not?

With respect.

(CID:128755023)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:12 AM . Last Modified: ‎2024-04-05 03:04 AM

0 Likes
0
557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:12 AM . Last Modified: ‎2024-04-05 03:04 AM

I have disabled the alarms for each rPDU. This was the only workaround I could use. I would have prefered to have a modify DDF so I don't have to disable the alarm every time I add a Serverteck rPDU.

Thanks

Enzo

 

(CID:128755169)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:12 AM . Last Modified: ‎2023-10-20 04:59 AM

0 Likes
0
557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:12 AM . Last Modified: ‎2023-10-20 04:59 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of