Posted: β2020-07-03 12:09 PM . Last Modified: β2024-04-08 02:34 AM
Hi all!
I have found a bug in StruxureOn GW 1.0.2.9: for the unclear reasons not all connected sensors (for example, dry contacts) to cascade connected NBRK0200+NBPD0150 are displayed. I.e. a part of sensors is displayed, and a part isn't. In StruxureOn GW is used signed DDF catalog Version 1.1.2.11-SNAPSHOT from December 19, 2016.
Very thanks for the support.
(CID:110790584)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 12:12 PM . Last Modified: β2024-04-08 02:33 AM
Dear Brian Behbehani,
I am glad to inform, that starting from the release of EcoStruxure IT Gateway 1.5.1.30, it became possible to view all sensors under NBRK0200+NBPD0150 devices. Great work!
Very thanks for the support.
The question is solved π.
(CID:138810942)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 12:09 PM . Last Modified: β2024-04-08 02:34 AM
Good Morning,
Sorry for the trouble that you are having with the SXon Gateway. Would you mind please giving me a little more detail. Are you not seeing all the information in the Gateway itself or the mobile app? If it is the mobile app are you seeing the name of the sensor, but the app shows a ' - ' where you expect the data? What kind of sensors are showing this information? This information will help us to troubleshoot and diagnose what you are seeing.
Thanks,
Rick
(CID:110791180)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 12:10 PM . Last Modified: β2024-04-08 02:34 AM
Hi Rick Ogren,
Are you not seeing all the information in the Gateway itself or the mobile app?
It is about web-interface of StruxureOn Gateway 1.0.2.9 with signed DDF catalog Version 1.1.2.11-SNAPSHOT from December 19, 2016.
What kind of sensors are showing this information?
For example, dry contacts NBES0304 and temperature/humidity sensors AP9335TH. And only a part above the specified sensors of both types is displayed (randomly). This statement is fair both for NBRK0200 and for NBPD0150 (two devices).
Very thanks for the support.
(CID:110792288)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 12:10 PM . Last Modified: β2024-04-08 02:34 AM
Hello,
I was wondering if you could possibly supply a screenshot of what you are seeing so I can get a better idea of what is going on? There is currently a bug logged against the AP9335TH not displaying temperature/humidity sensors, but I would like to see what is going on regarding the NBRK0200 and NBPD0150 sensors.
Thanks,
Nick
(CID:110795647)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 12:10 PM . Last Modified: β2024-04-08 02:34 AM
Hi Nicholas St. Pierre,
My currently work devices configuration is: NBRK0200+NBPD0150+NBPD0150 (under the names BVV1+BVV2+BVV3). In attachment I send two zip-files:
NBRK200.zip β screenshots of real configuration from web-interface of NetBotz;
SXOn_NBRK200.zip β screenshots the same NetBotz from StruxureOn web-interface.
Very thanks for the support.
(CID:110795848)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 12:10 PM . Last Modified: β2024-04-08 02:34 AM
It looks like the attachments may have been removed. You can try and re-send those attachments via email and hopefully we can figure out what's going on. Below is my direct email:
Nicholas.StPierre@non.schneider-electric.com
(CID:111414734)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 12:10 PM . Last Modified: β2024-04-08 02:34 AM
Hi Rick Ogren,
I report that in new release of SxOn GW 1.0.3.40 above the specified problem is still not solved. You can confirm?
Very thanks for the support.
(CID:115345161)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 12:10 PM . Last Modified: β2024-04-08 02:34 AM
Hi Rick Ogren and Nicholas St. Pierre,
I report again unfortunately, that in new release of SxOn GW 1.1.0.43 above the specified problem is still not solved. You can confirm?
Very thanks for the support.
(CID:124527600)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 12:10 PM . Last Modified: β2024-04-08 02:34 AM
Hi Rick Ogren and Nicholas St. Pierre,
I report again unfortunately, that in new release of SxOn GW 1.1.1.16 above the specified problem is still not solved. You can confirm?
Very thanks for the support.
(CID:125211690)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 12:10 PM . Last Modified: β2024-04-08 02:34 AM
Hi Rick Ogren and Nicholas St. Pierre,
I report again unfortunately, that in new releases of SxOn GW 1.1.2.25 and 1.1.3.9 above the specified problem is still not solved. You can confirm?
Very thanks for the support.
(CID:126176266)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 12:10 PM . Last Modified: β2024-04-08 02:34 AM
Hi Rick Ogren and Nicholas St. Pierre,
I report again unfortunately, that in new releases of SxOn GW 1.2.0.12 above the specified problem is still not solved. You can confirm?
However, starting with this new release, it became possible to perform discovering and monitoring of NetBotz appliance, for example, NetBotz-450. Great work!
Very thanks for the support.
(CID:126886996)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 12:11 PM . Last Modified: β2024-04-08 02:34 AM
Hello spezialist,
Can I get a screenshot of what you see in Gateway and what you see on the device. You can sent them to my email. Jason.Dutra@schneider-electric.com.
As mentioned in the other ticket After upgrade to SxOn GW 1.2.0.12 not posible monitoring and discovering the power meter "Asco G5 Group Controller" via Modbus interface? There is a targeted read function with StruxureOn but currently it is for modbus only. If necessary we can provide an SNMP walk tool you can run and send us the results for the time being.
(CID:128761491)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 12:11 PM . Last Modified: β2024-04-08 02:34 AM
Dear Jason Dutra,
The screenshots you are asking about can be found in my comment above for Nicholas St Pierre in this thread. Additionally, I send them to you in an e-mail. These screenshots a year ago (February 2017), but since then nothing has improved, i.e. the problem exists.
Thanks for clarifying about targeted read function with StruxureOn: now I understand, that this is only applicable to Modbus devices.
Very thanks for the support.
(CID:128761596)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 12:11 PM . Last Modified: β2024-04-08 02:34 AM
Hi Jason Dutra,
In the attachment of my e-mail, I send the requested snmpwalk file for this problem thread.
I thank you for your support and look forward to hearing.
(CID:128761957)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 12:11 PM . Last Modified: β2024-04-08 02:34 AM
Thank you spezialist I received your walk file and was able to simulate your device. I too am seeing the issue. I am unsure if it is a ddf or server side issue. I will push to have this addressed in an upcoming release.
(CID:128762121)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 12:11 PM . Last Modified: β2024-04-08 02:34 AM
Dear Jason Dutra,
I report again unfortunately, that in new release of EcoStruxure IT Gateway 1.3.0.48 above the specified problem is still not solved. You can confirm?
Very thanks for the support.
(CID:130090888)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 12:11 PM . Last Modified: β2024-04-08 02:33 AM
Dear Jason Dutra,
I report again unfortunately, that in new release of EcoStruxure IT Gateway 1.3.1.12 above the specified problem is still not solved. You can confirm?
Very thanks for the support.
(CID:130093480)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 12:11 PM . Last Modified: β2024-04-08 02:33 AM
spezialist I can confirm that this issue has not been addressed yet. Unfortunately, there has been other issues that have been deemed a higher priority for the moment.
Kind reagrds,
Jason
(CID:130093661)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 12:11 PM . Last Modified: β2024-04-08 02:33 AM
Dear Jason Dutra,
I report again unfortunately, that in new release of EcoStruxure IT Gateway 1.4.0.68 above the specified problem is still not solved...
Very thanks for the support.
(CID:134027096)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 12:12 PM . Last Modified: β2024-04-08 02:33 AM
spezialist We have identified the cause of the issue regarding dry contacts and will post a fix for that in 1.4.1 of the EcoStruxure IT Gateway, which is expected to be released within the next 2-3 weeks. Thank you for your patience.
(CID:134027443)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 12:12 PM . Last Modified: β2024-04-08 02:33 AM
I hope so, and I wait for fixes this bug.
Very thanks for the support.
(CID:134027486)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 12:12 PM . Last Modified: β2024-04-08 02:33 AM
Dear Brian Behbehani,
I am glad to inform, that starting from the release of EcoStruxure IT Gateway 1.5.1.30, it became possible to view all sensors under NBRK0200+NBPD0150 devices. Great work!
Very thanks for the support.
The question is solved π.
(CID:138810942)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 12:12 PM . Last Modified: β2023-10-22 03:07 AM