The Application is running but cannot log in.
What is the cause of this error and How to fix this?
(CID:144868826)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 07:57 PM . Last Modified: β2024-04-03 01:23 AM
Hi Tanawat,
Can you please add more details about this installation/setup.
Is it a usual/normal installation or customized installation?
did it work before?
what changes have been done just before appearance of the issue?
Kind regards
(CID:144868949)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 07:57 PM . Last Modified: β2024-04-03 01:23 AM
I have installed on VM last week and it works.
Only upload back up, restore and create a new floor plan.
Now root file system is used 99%.
(CID:144869203)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 07:57 PM . Last Modified: β2024-04-03 01:23 AM
Hi Tanawat,
It seems the sever dose not have enough resources such as storage capacity.
System requirements/recommendations are described here:
https://sxwhelpcenter.ecostruxureit.com/display/UADCO8x/System+requirements
I would recommend a clean installation, the minimum recommendation is 4 CPU, 16 GB RAM and at least 100 GB storage, and then restoring the latest backup file.
Please let me know, if you have questions, thanks.
Kind regards
(CID:144869252)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 07:57 PM . Last Modified: β2023-10-22 02:40 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.