Help reading a Natural Gas Totalizer on PME 8.2 - FCI ST80 64 bit double precision register

EcoStruxure Energy Hub

This forum is dedicated to supporting EcoStruxure Energy Hub service providers and partners with system implementation, reporting skills growth, and in demonstrating profitable improvements in monitored sites. Ask questions, get expert answers and the latest offer news, provide feedback and share community experience and knowledge!

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • EcoStruxure Energy Hub
  • Help reading a Natural Gas Totalizer on PME 8.2 - FCI ST80 64 bit double precision register
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Mathew_Losey
Lt. Commander Mathew_Losey Lt. Commander
5
Thierry_Baudard
Commander Thierry_Baudard Commander
5
Marcus_Gasper
Commander Marcus_Gasper Commander
4
CarolinaCastane
Commander CarolinaCastane Commander
4
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Power Monitoring Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Energy Hub
Solved
eskobar
Crewman eskobar
Crewman

Posted: ‎2024-08-21 11:48 AM

0 Likes
2
425
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-21 11:48 AM

Help reading a Natural Gas Totalizer on PME 8.2 - FCI ST80 64 bit double precision register

Good evening, everyone.

 

I kindly ask for your help in this matter, I'm an energy engineer with limited knowledge on industrial communications.

 

I am installing natural gas meters on my facility and I am having trouble getting the correct value from the modbus registers of an FCI ST80 unit.

 

I have this information:

eskobar_0-1724265738395.png

 

And this is the configuration I'm using on PME modbus device importer:

eskobar_1-1724265797860.png


The real totalizer is around 6,173,125 normal cubic meters and the value is in trillions ...

 

Thanks for your help.

 

 

Labels
  • Labels:
  • Knowledge Base
  • Tips and Tricks
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2024-09-05 08:08 AM

1 Like
0
373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-05 08:08 AM

Hello @eskobar , 

 

For standard Modbus, a register is codded on 16 bits:

  • If your value is UINT16/INT16 => you need 1 Modbus register to store your value.
  • If UINT32/INT32 => you need 2 Modbus registers.
  • If FLOAT32 => you need 2 Modbus registers
  • If UINT64/INT64 => you need 4 Modbus registers

Your document said that your device is using "Daniel" Modbus extension. In this case, a Modbus register is codded on 32 bits.

Romain_Polette_1-1725547679525.png

 

PME is not compatible with Daniel or Enron extension. 

 

Please try with the 4xxx registers listed in table 24 and keep in mind that your Less Significant and Most Significant bytes are inverted in your table.

Romain_Polette_2-1725547870693.png

Example: For your device, "Flow" is codded on 2x INT16 registers. Usually LS byte would be on 4100 and MS byte on 4101. But in your case, this is inverted. 

 

Try the following on PME DTE (I'm not sure for your Float 64 value...):

Romain_Polette_3-1725548869535.png

Regards, 

 

 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2024-09-05 08:08 AM

1 Like
0
374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-05 08:08 AM

Hello @eskobar , 

 

For standard Modbus, a register is codded on 16 bits:

  • If your value is UINT16/INT16 => you need 1 Modbus register to store your value.
  • If UINT32/INT32 => you need 2 Modbus registers.
  • If FLOAT32 => you need 2 Modbus registers
  • If UINT64/INT64 => you need 4 Modbus registers

Your document said that your device is using "Daniel" Modbus extension. In this case, a Modbus register is codded on 32 bits.

Romain_Polette_1-1725547679525.png

 

PME is not compatible with Daniel or Enron extension. 

 

Please try with the 4xxx registers listed in table 24 and keep in mind that your Less Significant and Most Significant bytes are inverted in your table.

Romain_Polette_2-1725547870693.png

Example: For your device, "Flow" is codded on 2x INT16 registers. Usually LS byte would be on 4100 and MS byte on 4101. But in your case, this is inverted. 

 

Try the following on PME DTE (I'm not sure for your Float 64 value...):

Romain_Polette_3-1725548869535.png

Regards, 

 

 

Romain POLETTE
Solution Architect - France Operations
Reply

Link copied. Please paste this link to share this article on your social media post.

eskobar
Crewman eskobar
Crewman

Posted: ‎2024-12-23 05:51 AM

1 Like
0
196
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-23 05:51 AM

For the record.

Thanks a lot, Romain. Your post helped me a lot to get the correct register.

Quite franlky, I didn't understood how the register in the document should be readed, the most significant and the less significant byte confused me, I thought they were separate register and values.

When you confirmed that Daniel / Enron were not supported on PME 8.2, I re-read the manual and understood that the correct register was:

 

4105 in F64 big endian. I tried it and corrected all the inverted registers and that worked.

Thank you very much.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of