This forum is dedicated to supporting EcoStruxure Energy Hub service providers and partners with system implementation, reporting skills growth, and in demonstrating profitable improvements in monitored sites. Ask questions, get expert answers and the latest offer news, provide feedback and share community experience and knowledge!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-21 11:48 AM
Good evening, everyone.
I kindly ask for your help in this matter, I'm an energy engineer with limited knowledge on industrial communications.
I am installing natural gas meters on my facility and I am having trouble getting the correct value from the modbus registers of an FCI ST80 unit.
I have this information:
And this is the configuration I'm using on PME modbus device importer:
The real totalizer is around 6,173,125 normal cubic meters and the value is in trillions ...
Thanks for your help.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-09-05 08:08 AM
Hello @eskobar ,
For standard Modbus, a register is codded on 16 bits:
Your document said that your device is using "Daniel" Modbus extension. In this case, a Modbus register is codded on 32 bits.
PME is not compatible with Daniel or Enron extension.
Please try with the 4xxx registers listed in table 24 and keep in mind that your Less Significant and Most Significant bytes are inverted in your table.
Example: For your device, "Flow" is codded on 2x INT16 registers. Usually LS byte would be on 4100 and MS byte on 4101. But in your case, this is inverted.
Try the following on PME DTE (I'm not sure for your Float 64 value...):
Regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-09-05 08:08 AM
Hello @eskobar ,
For standard Modbus, a register is codded on 16 bits:
Your document said that your device is using "Daniel" Modbus extension. In this case, a Modbus register is codded on 32 bits.
PME is not compatible with Daniel or Enron extension.
Please try with the 4xxx registers listed in table 24 and keep in mind that your Less Significant and Most Significant bytes are inverted in your table.
Example: For your device, "Flow" is codded on 2x INT16 registers. Usually LS byte would be on 4100 and MS byte on 4101. But in your case, this is inverted.
Try the following on PME DTE (I'm not sure for your Float 64 value...):
Regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-12-23 05:51 AM
For the record.
Thanks a lot, Romain. Your post helped me a lot to get the correct register.
Quite franlky, I didn't understood how the register in the document should be readed, the most significant and the less significant byte confused me, I thought they were separate register and values.
When you confirmed that Daniel / Enron were not supported on PME 8.2, I re-read the manual and understood that the correct register was:
4105 in F64 big endian. I tried it and corrected all the inverted registers and that worked.
Thank you very much.