Cooling Configuration Accuracy and Design Guidelines

Configuring cooling

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • IT Advisor
  • ITA desktop client
  • Configuring the ITA desktop client
  • Configuring cooling
  • Cooling Configuration Accuracy and Design Guidelines
Options
  • Subscribe to RSS Feed
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • EcoStruxure IT forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to Configuring cooling
Options
  • Subscribe to RSS Feed
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
843 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Cooling Configuration Accuracy and Design Guidelines

Picard EcoStruxureIT
‎2019-11-06 07:13 AM

Cooling configuration accuracy

The Potential Flow Models (PFM) used in this application are typically within about 10% of CFD for Capture Index, Average Rack Inlet Temperature, and perforated tile airflow; they are not as good at predicting maximum rack inlet temperatures.

Cooling design guidelines

For the most efficient cooling design, equipment should be placed in clusters. An equipment cluster is two nearly-equal-length rows of equipment separated by a hot or cold aisle. A row of equipment can be a member of one or two clusters.

All heat generating equipment (racks and UPS) properly positioned in rows will show up color-coded in the Floor layout. However, you will experience better cooling performance with well formed clusters:

  • All rows are of similar length and aligned across hot or cold aisles.
  • The equipment rows do not include blocks, gaps, or spaces.
  • In Hot Aisle Containment Systems (HACS), cooling units are positioned in pairs directly across from each other.

Example: Well formed cluster

102237742_360037994714.png102237742_360037994714.png

Cooling performance predictions, which assume the racks are populated evenly, will be more accurate if racks are populated in bottom-to-top order and for more regular room shapes and well-formed hot/cold aisle layouts.

Note

If you flip a row to face front to back, it affects the cooling simulation for up to 3 rows.

Cooler airflow specifications

  • Cooler airflow in cubic feet per minute (CFM) is assumed to be:

    Cooler type

    Minimum CFM

    Maximum CFM

    InRow RC (300 mm)

    1450

    2900

    InRow RC (600 mm)

    2760

    6900

    InRow RP (600 mm Chilled Water)

    2760

    6900

    InRow RP (600 mm Air Cooled)

    1920

    4800

    InRow RD (600 mm Air Cooled)

    2000

    5000

    InRow RD (300 mm Air Cooled)

    916

    2300

    InRow RD (300 mm Fluid Cooled)

    916

    2300

  • Rack airflow is by default assumed to be 160 CFM/kW based on the total rack power. This value can be changed by right-clicking a rack and selecting Properties, to change to, for example, 105 CFM/kW for blade server racks.
  • CRAC airflow is, by default, assumed to be 6000 CFM. This can be changed by right-clicking a CRAC and selecting Properties.
  • UPS airflow is automatically calculated by the system based on the UPS size and the number of power modules (assumed to be 10kW each).
  • Airflow through each tile is calculated as the tiles are positioned in the layout.
  • Airflow for generic powered equipment is not included in the cooling calculations by default. This can be changed by right-clicking a piece of generic powered equipment and selecting Properties.
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

Didn't find what you are looking for? Ask our Experts
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of