Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Optimizing the Cooling Configuration Accuracy by Adjusting Power and Cooling Estimates

Configuring cooling

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • IT Advisor
  • ITA desktop client
  • Configuring the ITA desktop client
  • Configuring cooling
  • Optimizing the Cooling Configuration Accuracy by Adjusting Power and Cooling Estimates
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • EcoStruxure IT forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to Configuring cooling
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
411 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Optimizing the Cooling Configuration Accuracy by Adjusting Power and Cooling Estimates

Picard EcoStruxureIT
‎2019-11-06 07:13 AM

Optimizing the cooling configuration accuracy by adjusting power and cooling estimates

Since IT Advisor uses estimates to calculate the temperatures in the 3D view, you cannot expect the simulation to be completely accurate.

However, you can improve the accuracy of these estimates to fit your particular setup by providing the system with as much information about the power and cooling in your data center as possible.

Server load estimates

In IT Advisor, every server in the data center has two power estimates.
By default, the two values are the same. They define the maximum power consumption for a particular server in its maximum configuration.

  • Manufacturer's Nameplate: Identifies the nameplate value of the selected server. IT Advisor uses this value as the reference value.
  • Estimated Load: Identifies the estimated load of the selected server. IT Advisor uses this value for the calculations.

You can lower the Estimated Load for all servers in the data center if they do not consume all the power specified by the nameplate value.
The option is available if you right-click the server and select Properties>Power.

Cooling unit airflow estimates

The accuracy of the cooling unit airflow is about 85-90% in typical configurations.

However, you can adjust the airflow properties for the cooling units if the default values in the system do not match your specific setup.
The option is available if you right-click the cooling unit and select Properties>Cooling.

In this way, you can provide the system with the specific power and cooling values for your data center and improve the accuracy of the configuration.

Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

Didn't find what you are looking for? Ask our Experts
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now