WebClient most common installation problems

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • WebClient most common installation problems
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • JonGreen
    JonGreen
  • Alan_Wood
    Alan_Wood
  • DavidFisher
    DavidFisher
  • ScottLeedberg
    ScottLeedberg
  • Jonathan
    Jonathan
  • AdamSteele
    AdamSteele
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5575 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

WebClient most common installation problems

Picard Product_Support
‎2018-09-07 01:49 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 03:12 AM

Issue

WebClient most common installation problems

Product Line

Andover Continuum

Environment

  • Continuum webClient Server
  • Microsoft IIS
  • Microsoft .NET Framework

Cause

WebClient is not functioning properly. Troubleshooting steps are required.

Resolution

Below are some of the more common problems that Technical Support runs into when troubleshooting a WebClient installation.

Microsoft DCOM settings (Manually setting up DCOM was needed prior to version 2.0)

This is the most common problem that PSS runs into. There are two areas that these settings need to be set in are, “Access Permissions” and “Launch and Activation permissions”. Incorrect DCom settings in WebClient will cause many different problems. It could cause problems with logging into the system, opening graphics, seeing the Active Alarm view, etc… The users that should be in there are below for Windows 2000 IIS and Windows XP IIS servers:

INTERACTIVE SYSTEM

  • ComputerName\IUSR_ComputerName (Internet guest account)
  • ComputerName\IWAM_ComputerName (Launch IIS process account)
  • ComputerName\ASPNET (ASP.NET)

Additionally for Windows 2003 IIS servers this additional user is needed:

  • ComputerName\NETWORK_SERVICE

To help pinpoint the DCOM permission that is not set properly, consult the steps at Identify which DCOM permission are causing DCOM errors when trying to use WebClient.

Microsoft .Net Frame work Zone Permissions

This is another one of the more common problems in WebClient installs. Not setting the .Net Zone permissions correctly will cause problems with opening schedules in the WebClient browser machines. The .Net zone permissions has to be set on each client browser. See the section in the WebClient install guide on setting the .Net Zone permissions.

Microsoft .Net Framework is installed before the IIS is installed

If .Net is installed prior to IIS you will see problems with logging into the system, editors may not work, schedules will not be able to be opened. If there is any doubt to whether or not .Net was install before the IIS then open a Windows command prompt and run the below commands.

  • For Windows 2000 Professional it is:
    c:\WinNT\Microsoft.NET\Framework\v1.1.4322\aspnet_regiis.exe -i
  • For Windows XP Professional, Windows Server 2003 it is:
    c:\windows\Microsoft.NET\Framework\v1.1.4322\aspnet_regiis.exe -i
  • For Windows10/Windows7/Server2003 it is:
    c:\Windows\Microsoft.NET\Framework\v2.05.50727\aspnet_regiis.exe -i
  • Also, Windows10/Windows7/Server2003 using 1.94 SP1 and greater, .net 4.x is used 
    c:\Windows\Microsoft.NET\Framework\v4.0.30319\aspnet_regiis.exe -i
    Run both 2 and 4 commands 

Microsoft .Net 2.0

This is not supported until V1.74 and will cause problems with WebClient. You will see problems with reports, schedules on earlier versions. SQL Authentication methods with WebClient The only authentication method for SQL server that WebClient supports is SQL Server and Windows. Due to the methods we use to access data in the SQL database with WebClient the authentication must be set this way.

Internet Information Server Secure Sockets Layer (IIS SSL)

Currently using SSL with WebClient is not supported in versions prior to V1.74.

Remote installs of WebClient due to underlying Microsoft Security a WebClient cannot be installed through any kind of remote terminal services, or RDP. If the system is installed through remote services there will be security problems with accessing WebClient. The correction to these problems is to be directly on the WebClient / IIS machine and uninstall all the WebClient apps, Microsoft .Net, and Microsoft IIS then re-install the applications per our instructions while directly on the WebClient machine.

Remote reboots of a WebClient IIS server

If you use a remote terminal service and reboot and log on to an IIS server running WebClient you will run into problems with logging into WebClient. (webclient is unavailable error)

If using VMWare with 2.0 and above, use the VMWare Open console feature

Multiple Network cards in the IIS server

Using multiple network interface cards in an IIS server is not supported. Doing this will cause problems with opening graphics through WebClient.

Installation of files on the Client browsing machines

The first time WebClient is accessed through a browser, either in new installs or upgrades, files need to be installed on that client browser machine. You will need to be logged in with a Windows user that has the permissions to install software. Install of WebClient on the IIS computer while virus scan software is running. Make sure that when installing WebClient, either new installs or upgrades, that any virus scan software is disabled. In some instances virus scan software has caused problems with WebClient installs or upgrades.

"&" characters in names of objects

Ampersands are special characters in web browsing and should not be used in anything in Continuum that the WebClient browser will have access to. Some of the problems that have been seen are alarms not showing up in the Active Alarm view and not being able to add areas to personnel objects.

Setting up WebClient graphics

Once WebClient is installed on the IIS server you need to make sure you open CyberStation Pinpoint and set the “Web Locations” for your graphics sharing. If you do not set this you will not be able to access graphics through WebClient. When these are set incorrectly you will see a red “X” next to the path.

Ports used in WebClient

Until V1.74 we only support the use of Port 80 in WebClient. CyberStation on the IIS WebClient server. In order for WebClient to function properly the CyberStation that is installed as part of the WebClient install on the IIS server must be running. You do not need to be logged on to the CyberStation it just needs to be running.

WebClient graphics and firewalls

Prior to 1.73 there were some special installation considerations when dealing with customers that had browsing machines both inside and outside a firewall. In the 1.73 WebClient there is no special installation/configuration that needs to be done. The system can be set up as if all the browsers are on the local network.

Renaming or changing the Domain of the IIS Server after IIS is installed

Renaming or changing the Domain that the IIS server was initially installed with will cause problems with IIS which in turn will cause problems with WebClient. If this has to be done then you will need to uninstall webclient before name change and then re-install webclient.

Directory Browsing setting for WebClient graphics

In some instances where the Windows security on the IIS server is restrictive you will need to add “Directory Browsing” to the NewGraphicsFiles share in the web site configuration on the IIS Server.
In webclient 2.0 and greater, directory browsing is configured during the installation.

Using underscores or hyphens in the name of the IIS Server

This will cause problems with the operation of WebClient because those characters are special characters in the application.

Labels (1)
Labels:
  • Andover Continuum
Tags (8)
  • Find more articles tagged with:
  • 2155
  • AlanWood19
  • andover
  • continuum
  • dotnet
  • explorer
  • internet explorer
  • webclient
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore