Using Loytec LPA with SpaceLogic Server AS-P

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Using Loytec LPA with SpaceLogic Server AS-P
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • DavidFisher
    DavidFisher
  • MikaelKrantz
    MikaelKrantz
  • Product_Support
    Product_Support
  • RyanSuar
    RyanSuar
  • LeeCravens
    LeeCravens
  • Benji
    Benji
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3103 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Using Loytec LPA with SpaceLogic Server AS-P

Picard Product_Support
‎2018-09-11 02:50 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 10:08 PM

Issue

How can you use Loytec's LPA software with the AS as the interface

Product Line

EcoStruxure Building Operation

Environment

  • Automation Server
  • Loytec LPA

Cause

A Loytec LPA can be a valuable troubleshooting tool to diagnose communication problems on a LON Fieldbus.

Resolution

As the Automation Server uses Loytec's Lon chip, it is possible to use Loytec's LPA software over the Lon port on the AS.

Some Prerequisites:  

  1. A license is required to use the LPA software. Either the "LPA-IP" or the "LPA-IP-SW" package depending on your setup.
  2. LPA (loytec.com) shows a product overview.  
  3. Downloads | Software - Device Firmware and Readme (loytec.com) to download the software. Create a free login in order to download software from Loytec's home page
  4. For additional help
    1. Buying and registering the LPA software read LonTalk Protocol Analyzer Software License and Registration Steps
    2. Lonworks troubleshooting read Troubleshooting LON Network Communication
    3. Troubleshooting Lon communication with TAC Xenta's read Actions for reducing Bandwidth in a Vista network
  5. There is a limitation when using LPA through an AS. Refer to Not all traffic on a segment is captured when using the LPA through an Automation Server
  6. Please make sure that you have a LonWorks interface configured in the Automation Server before proceeding. You will also need to add a Local Node to the interface and to commission it.
  7. Make sure to set the LPA state to Enabled under the Advanced tab in the properties for the LonWorks Interface:LPA Enabled.png

Once the above have been checked and understood the following steps can be performed:

 

  1. Start the LPA software
  2. Click on "Profile -> Network Interface..."
  3. Click on "Remote LPA Assignment"
  4. Click on "Add Device"
  5. Enter the IP address of the Automation Server, click on "Get Info" and click on "Add Device and Restart Search"
  6. Select the Automation Server device and click on "Assign/Add"
  7. Select the interface you want to assign to the Automation Server, and click "Assign"
  8. With the interface assigned, click "OK"
  9. Select the Building Operation interface and click "OK"
  10. Now the LPA software is using the Automation Server as the interface
  11. Start a new LPA log
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • 16285
  • MikaelKrantz22
  • RobertAndriolo22
Was this article helpful? Yes No
100% helpful (3/3)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore