TAC Vista installations prior to TAC Vista 5.0.1 cannot be upgraded to TAC Vista 5.1.9  version directly.
TAC Vista
  • TAC Vista Server
  • TAC Vista Workstation
When upgrading Vista to 5.1.9, certain steps need to be followed to ensure that the process works properly.
Note: If upgrading from an older version of Vista where the LNS port is at the root level of the system tree, instead of underneath the Vista Server, then you will need to follow the steps in Graphics binding were broken after a Vista upgrade to 4.5 from an earlier version to fix the binding paths of root level objects.
TAC Vista installations between 4.3.0 and 5.0.0 must follow these upgrade steps in order:
  1. Upgrade to a version between 5.0.1 and 5.1.6
  2. Upgrade to version 5.1.9
TAC Vista installations prior to 4.3.0 must follow these upgrade steps in order:
  1. Upgrade to a version between 4.3.0 and 5.0.0
  2. Upgrade to a version between 5.0.1 and 5.1.6
  3. Upgrade to version 5.1.9
Note: In a situation with multiple databases on a computer, make sure all are upgraded in this manner. After the upgrades have been carried out make sure the master server is started first followed by the slave servers.