Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

MSMQ issue causes Alarms and Access Event delivery problems between CyberStations

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • MSMQ issue causes Alarms and Access Event delivery problems between CyberStations
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • AdamSteele
    AdamSteele
  • SangKim
    SangKim
  • CraigEl
    CraigEl
  • AbeMeran
    AbeMeran

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2976 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

MSMQ issue causes Alarms and Access Event delivery problems between CyberStations

Picard Product_Support
‎2018-09-11 08:51 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 07:59 PM

Issue

Continuum running under MS Windows 7, Vista or MS Windows Server 2008 (including R2)

Access event viewers at workstations other than the primary access server do not show events.

Alarms acknowledged at one CyberStation would remain unacknowledged in the other CyberStations. 

Product Line

Andover Continuum

Environment

  • CyberStation
  • Microsoft Windows 7
  • Microsoft Windows Server 2008
  • Microsoft Windows Server 2008 R2

Cause

Problem in Microsoft MSMQ component.

MSMQ service might not send or receive messages after you restart a computer that is running Windows 7, Windows Server 2008 R2, Windows Vista or Windows Server 2008.

This will cause any Continuum component that uses MSMQ (such as Alarms and Access Events) to fail.

Microsoft has issued a hot fix for this MSMQ problem.

Resolution

Use the following command prompt test to verify the problem
netstat -ano | findstr 1801
The command tests whether MSMQ is listening for messages.

For example, Continuum WS 'A' is the primary access server (PAS) with an Event Viewer 'EV' up,  a second Continuum WS 'B'  is also displaying the same EV.

If MSMQ is functioning normally you should see the following.

1. is the IP address of WS 'B' that has established a link to WS 'A' 

2. is the IP address of WS 'A', the PAS in this case.

2560 is the listening MSMQ process PID 

You can clearly see that there is a MSMQ process (2560) in WS 'B' LISTENING on port 1801

If there is no MSMQ process listening the output of the command will show the loopback or localhost IP address 127.0.0.1

and you have to install the following Microsoft hotfix:

Package:

-----------------------------------------------------------

-----------------------------------------------------------

See Microsoft KB Article Number: 2554746

 

** In very rare occasions, removing MSMQ and adding MSMQ again to the PC is required.

** Once it is re-installed, please refer to Access event viewers running in a workstation other than the Primary Access Server stop displaying e... to set the MSMQ CleanupInterval setting to one hour in the primary access server.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 13192
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore