Access event viewers running in a workstation other than the Primary Access Server stop displaying events

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Access event viewers running in a workstation other than the Primary Access Server stop displaying events
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • Alan_Wood
    Alan_Wood
  • Chris_Asbury
    Chris_Asbury
  • BillNeville
    BillNeville
  • CraigEl
    CraigEl
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2705 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Access event viewers running in a workstation other than the Primary Access Server stop displaying events

Picard Product_Support
‎2018-09-11 03:54 AM

Last Updated: Admiral Alan_Wood Admiral ‎2022-11-04 07:30 AM

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance.

Issue

Access Event Viewer running in a CyberStation other than the primary access server works initially but after some period of time stops displaying access events.

Product Line

Andover Continuum

Environment

  • CyberStation
  • MSMQ

Cause

Product support has identified several scenarios that can result in Cyberstations other than the primary not showing events in the Live Event Viewer. The commonality with all these cases is that the Primary Access Server(PAS) will always show the events, so before using any of the solutions specified below make sure that is ONLY workstations other than the PAS that are not displaying events in their Live Event Viewer

 

NOTE also, that we are referring strictly to the Live Event Viewer in this article so it is assumed events are showing in a list view including the Access Events tab that shows events in the door's editor.

 

CAUSE #1 (Primary failed over to Secondary then back to Primary)

In systems configured with a Primary and secondary Access Server (SAS), it has been found that after a failover to the SAS due to the PAS going offline, event viewers in other workstations continue to show events UNTIL the PAS WS returns online and resumes its role of PAS at which point all workstations (other than the PAS) stop displaying events in their Live Event Viewers.

 

CAUSE #2 (MSMQ issue reported and fixed by Microsoft)

Continuum running under MS Windows 7, Vista or MS Windows Server 2008 (including R2)

Access event viewers at Cyberstations other than the PAS do not show events.

Alarms acknowledged at one CyberStation would remain unacknowledged in the other CyberStations. 

Please see MSMQ issue causes Alarms and Access Event delivery problems between CyberStations for more information.

 

ISSUE #3

MSMQ CleanupInterval setting is too short.

Resolution

SOLUTION #1

  • First, make sure the ControllerStatus notification object is configured to send the offline alarm to all the Workstations in question.
  • Second, put a PE program in the SAS to serve as a monitor to let the Live Event Viewer know when the PAS has returned online, this is accomplished by referencing an object from the PAS

 SAMPLE PE POGRAM

SOLUTION #2  (MSMQ issue reported and fixed by Microsoft)

Click MSMQ issue causes Alarms and Access Event delivery problems between CyberStations for more information.

 

SOLUTION #3

In the Windows registry add the key \SOFTWARE\Microsoft\MSMQ\Parameters\CleanupInterval

The recommended setting is 3600000 which is the number of milliseconds in an hour

 

For additional information about the CleanupIntervalKey, see the following article from Microsoft:

http://msdn.microsoft.com/en-us/library/ms703235(VS.85).aspx

Labels (1)
Labels:
  • Andover Continuum
Tags (8)
  • Find more articles tagged with:
  • 13266
  • access events
  • active
  • AlanWood22
  • event view
  • eventview
  • live
  • msmq
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of