How to check and stop Event data filling up Building Operation Reports Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to check and stop Event data filling up Building Operation Reports Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
531 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to check and stop Event data filling up Building Operation Reports Server

Picard Product_Support
‎2018-09-11 11:39 PM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:36 AM

Issue

Log data is not being logged into SQL.

The Reports Server indicates that the database is full.  

This view will be shown when logging into the WebReports interface. If this chart is not shown, the PC is not running an Express edition of SQL.

Product Line

EcoStruxure Building Operation

Environment

Reports Server

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance.

Cause

In most instances, the data that quickly fills the SQL database are Events. Event data fills the SQL Database and prevents log data from passing to the Reports Server database. If the data has filled within a few days, this would indicate an issue, and contacting your local support is the best option here. The Process below allows the user to stop the reporting agent from passing specific information to the Reports Server.

If the data files are due to the amount of data stored, then an upgrade to the Standard/Full version of SQL is recommended.  

Resolution

To verify that the Events table is the likely cause of the SQL filling up, there are Standard Reports in the later versions of SQL.  The below example uses SQL Server version 13.x and shows the "Disk Usage by Top Tables."  
SXRDB-TableUsage.png
If the Standards Reports are not available, then use the following article Building Operation Reports SQL Database Full, for instructions on how to show the details for each table.
   
The Process below allows the user to stop the reporting agent from passing Event information to the SQL Database:
  1. Download the latest SBO Reports Agent Config tool from the community.
  2. Load the Tool onto the Reports Server PC.
  3. Stop the Reporting Agent Using the Tool
  4. Press F7 to get to the Advanced Agent Configuration Page
  5. Change the numEventRecordToRead property to 0. This will prevent future event data from being written to the Reports Server database.
  6. Press Ok
  7. Under the Maintenance tab of the tool - there are two options under Events 
    1. Delete future events, alarms, and trends 
    2. Delete events and alarms older than...
      SBOReportAgentMaintenenceEvents.png
  8. Restart the Reporting Agent

This will stop any further Events from being passed through to the SQL Database.  

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • 18326
  • RobertAndriolo24
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore