Building Operation Report Server SQL Database Full

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Operation Report Server SQL Database Full
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
6579 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Building Operation Report Server SQL Database Full

Picard Product_Support
‎2018-09-11 02:54 PM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:36 AM

Issue

SQL Database is full, or the partition the SQL is installed is full

Product Line

EcoStruxure Building Operation

Environment

Building Operation Report Server

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance.

Cause

If a site is using SQL Express 2008, the limit is 10 GB. If using the full version(s), it is unlimited. If the database or the partition where the Reports Server resides is full, here are some steps to reduce the SQL table volume and offer a short-term solution.

Resolution

  1. Before continuing, make sure there is a good backup of the database.
  2. Using SQL Server Management Studio, highlight the StruxureWareReportsDB and select New Query
  3. Use the following Script in that Query:
    SELECT t.NAME AS TableName, s.Name AS SchemaName, p.rows AS RowCounts, 
    SUM(a.total_pages) * 8 AS TotalSpaceKB, SUM(a.used_pages) * 8 AS UsedSpaceKB,
    (SUM(a.total_pages) - SUM(a.used_pages)) * 8 AS UnusedSpaceKB
    FROM sys.tables t INNER JOIN sys.indexes i ON t.OBJECT_ID = i.object_id
    INNER JOIN sys.partitions p ON i.object_id = p.OBJECT_ID AND i.index_id = p.index_id
    INNER JOIN sys.allocation_units a ON p.partition_id = a.container_id
    LEFT OUTER JOIN sys.schemas s ON t.schema_id = s.schema_id
    WHERE t.NAME NOT LIKE 'dt%' AND t.is_ms_shipped = 0 AND i.OBJECT_ID > 255
    GROUP BY t.Name, s.Name, p.Rows ORDER BY t.Name
  4. Select Execute to run that Query as shown in the screen capture below:
  5. The Results show each of the tables and the size of those tables as shown in the screen capture below:
  6. Purely for example purposes, a script to reduce the number of Events would be
    delete from tbEvents where DATEDIFF(day, datetimestamp, getdate()) > 180
  7. To gain back the space after deleting rows, right-click on StruxureWareReportsdb > Tasks > Shrink > Database
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (7)
  • Find more articles tagged with:
  • 16310
  • capacity
  • column
  • columns
  • oversized
  • remove
  • RobertAndriolo24
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore