Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

How Continuum determines if an Infinity Controller node is offline.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How Continuum determines if an Infinity Controller node is offline.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • David_Kendrick
    David_Kendrick
  • BillNeville
    BillNeville
  • JohnBoehmer
    JohnBoehmer
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2891 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How Continuum determines if an Infinity Controller node is offline.

Picard Product_Support
‎2018-09-06 12:13 PM

Last Updated: Sisko GavinHe Sisko ‎2023-05-23 03:02 AM

Issue

What has to happen for CyberStation to generate an offline controller alarm.

Product Line

Andover Continuum

Environment

  • CyberStation
  • Infinity Controller
  • Offline alarms

Cause

Receiving offline controller alarms yet controller appears to be online.

Resolution

Controllers can be offline for many reasons, such as a broadcast storm or will not come online, but consider the following points:

  1. In order to determine whether a controller is offline, a CyberStation will send out a probe to the controller.  
  2. The frequency with which CyberStation sends out the probe is determined by the value of the Probe Time field on the General Page of the workstation configuration.
  3. If an Infinity Controller does not respond to a probe, CyberStation will wait until a probe can be sent to all other Infinity Controller nodes in the system. 
  4. If the controller fails to respond to a second probe the controller is designated as Offline by CyberStation.
  5. Each CyberStation evaluates the commstatus of all controllers and reports alarms to the database.  Occasionally a CyberStation will show a controller as being offline while another CyberStation will show the same controller in an online state.
  6. When more that one workstation detects that the same controller is offline, this information is negotiated so that there will normally not be multiple offline alarms for the same controller.  Some versions of Continuum handle this better than others. 
  7. When an offline controller responds to a probe it is marked as Return to Normal. The controller may also be marked as Return to Normal if the workstation receives some other communication from the controller.
Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 8193
  • DavidKendrick23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.