Error when viewing Graphic panel in Pinpoint. "Pinpoint: Failed to call pILiveData->GetLiveData(). ACDataServices has an error."
  • Error when viewing Graphic panel in Pinpoint. "Pinpoint: Failed to call pILiveData->GetLiveData(). ACDataServices has an e...
  • Alan_Wood
    Alan_Wood
  • RandyDavis
    RandyDavis
  • AdamSteele
    AdamSteele
‎2018-09-06 12:56 PM
Last Updated: Administrator CraigEl Administrator ‎2025-05-07 06:53 PM
General Continuum instability is followed by the following error when viewing Graphic panels.
Andover Continuum
Continuum Cyberstation
Continuum has become unstable due to modules not starting up properly. This can be evidenced by looking at the Windows Application Event Logs for "Send Email" errors when alarms occur. This may then be followed by Continuum applications starting to crash and post errors.
  • Remove "email" and "page" entries in Event Notifications if there has not been an Email client installed and configured to email alarms.
  • Set Windows virtual memory settings to 4096.
  • Ensure time synchronization between Cyber and CX.
  • In Continuum General preferences set the Time Interval Between Requests to 100 (default is 30).
  • Set COV increment for noncritical points to non-zero numbers (default is 0).
  • Upgrade to 2.03. If already at 2.03, a reinstall of Continuum may be necessary or at least the pre-requisite 'Visual C++ 2005 redistributable'.
Also refer to: Crash of ACCDataServices on start-up or run
Tags (3)
  • 6853
  • AlanWood22
  • AlanWood25