Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

ES will not start due to no valid license or Cannot find license file error

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • ES will not start due to no valid license or Cannot find license file error
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • DavidFisher
    DavidFisher
  • Robert_Davis
    Robert_Davis
  • sesa139513
    sesa139513
  • sesa119747
    sesa119747
  • LeeCravens
    LeeCravens
  • Benji
    Benji
  • StephenYang
    StephenYang
  • Cody_Failinger
    Cody_Failinger
  • AbeMeran
    AbeMeran
  • sesa177673
    sesa177673

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
10284 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

ES will not start due to no valid license or Cannot find license file error

Picard Product_Support
‎2018-09-10 01:32 PM

Last Updated: Administrator CraigEl Administrator ‎2023-10-19 04:25 PM

Issue

Enterprise Server will not start due to no valid license file error: "nsp.csc.licensemanager No valid Enterprise Server license found. Terminating server."

SoftwareAdministrator.png

or Cannot find license file. (Error code: -1)

LicenseErrorCode-1.png

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Software Administrator
  • Building Operation License Administrator
  • Building Operation Workstation

Cause

Enterprise Server is not started and states no valid license file is found. License Server is installed on the same computer and has valid license(s).

Similarly, WorkStation may not start even with a License Server installed with a valid license.

If you get error -1, it means that you didn't enter the required @ before the license server address.

Resolution

In general, any licensed Building Operation software (Enterprise Server, WorkStation, Editors) needs to know where the license server is located. That means that the license server path needs to be entered on any PC having licensed Building Operation software installed.

The "License Administrator" part of the license installer can be installed on any PC, and the license server address set using the administrator. The license server itself does not need to be installed on all PC's, but only on the PC hosting e.g. the Enterprise Server.

The IP or DNS name of the PC hosting the license server is entered with an initial @, e.g. if the IP of the license server PC is 1.2.3.4 you enter @1.2.3.4

Checkpoints

  1. Remember to enter the license server address starting with a @. For example, don't use "localhost" but "@localhost".
  2. Is your evaluation license current? If not, download from EcoXpert Extranet
  3. Check that antivirus software is configured to allow the operation of the license server. (refer to SmartStruxure Workstation or editors can't get license when using firewall (errors -15 or -96))
  4. Reboot the machine where the License Server is running. It has been observed in some cases where the error 'No valid license or Cannot find license file error' appeared after an upgrade that rebooting the machine solves the problem.
  5. Check to see if there are multiple versions of the License Server installed on the machine. If multiple versions are installed, make sure to only run the highest installed version as a Windows Service. All other License Server and License Administrator software should be uninstalled from the machine.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (5)
  • Find more articles tagged with:
  • 11483
  • nsp.csc.licensemanager
  • RobertDavis20
  • StephenYang23
  • terminating
Was this article helpful? Yes No
75% helpful (3/4)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore