EcoStruxure Workstation or editors can't get license when using firewall (errors -15 or -96)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • EcoStruxure Workstation or editors can't get license when using firewall (errors -15 or -96)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
4 Likes
21629 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

EcoStruxure Workstation or editors can't get license when using firewall (errors -15 or -96)

Picard Product_Support
‎2018-09-11 07:47 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:49 AM

Issue

When PC based firewall's are used, some configuration in the license system and in the firewall are required to be made.

In some cases, the error below when logging into Workstation appears:
License server machine is down or not responding (Error code -15 or -96)

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Workstation

Cause

The TAC license (taclic) vendor daemon by default uses a random port each time it's started. This setting makes it difficult to handle in a firewall. Also the various EcoStruxure programs using the license system needs to be allowed in the firewall, as well as the ports used by the license system.

Here is a simple explanation of how the license request from a client is made.

Resolution

Make sure there is a valid license installed on the license server. For more information read Requested license not available for Enterprise Server, Workstation or editors


The easiest way to configure Windows firewall, is to run the SBO Firewall Config tool on all PC's having EcoStruxure software installed. For any questions regarding the use of this tool please contact the developer, details in the tool.


In order to manually make the configuration follow the steps below. For more information on how to create Windows firewall rules, read Creating Inbound and Outbound Windows Firewall Rules.

 

On the server PC

  1. Make the port used by the vendor daemon fixed. Follow Define the port used by the taclic vendor daemon guide to do that.
  2. On the PC having the license server installed, open the following TCP ports in the firewall both inbound and outbound. 
    • 80
    • 443
    • 4444
    • 2170
    • 27000 through 27009

(If a user defined defined port has been used other than 2170 for the vendor daemon then use that instead of 2170)

 

On the client PC

  1. On the PC having EcoStruxure software installed using the license server on a remote PC, make these exceptions in the firewall: Allow ports TCP 80, 443, 4444, 2170 and TCP 27000 through 27009 both inbound and outbound. (If you defined a port other than 2170 for the vendor daemon then use that instead of 2170)
  2. Allow the following programs:
    • SE.Graphics.Editor.exe
    • SE.SBO.Script.Editor.Proxy.exe
    • SE.SBO.ScriptEditor.exe
    • SE.SBO.WorkStation.exe
    • SE.WorkStation.IA.WptEd.exe
    • tam32.exe

They are typically located here:

  • On 32 bit OS:
    C:\Program Files\Schneider Electric StruxureWare\Building Operation 1.X\WorkStation
  • On 64 bit OS:
    C:\Program Files (x86)\Schneider Electric StruxureWare\Building Operation 1.X\WorkStation
Labels (1)
Labels:
  • EcoStruxure Building Operation
Attachments
Tags (6)
  • Find more articles tagged with:
  • 16184
  • available
  • ChrisAsbury22
  • reports
  • requested
  • virtual
Was this article helpful? Yes No
100% helpful (7/7)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore