Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Communications troubleshooting in SmartStruxure

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Communications troubleshooting in SmartStruxure
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Carl_Slack
    Carl_Slack
  • RobertAndriolo
    RobertAndriolo
  • CraigEl
    CraigEl
  • Cody_Failinger
    Cody_Failinger
  • sesa177673
    sesa177673
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3425 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Communications troubleshooting in SmartStruxure

Picard Product_Support
‎2018-09-11 08:49 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 06:29 PM

Issue

The built in logs for troubleshooting communications from SmartStruxure ES/AS to SmartStruxure ES/AS remove the need for network captures for SmartStruxure communications. However, SmartStruxure to BACnet continues to be ideal for traditional means of network captures. The most common capture method is Wireshark when dealing with BACnet device to BACnet device communication.

Product Line

EcoStruxure Building Operation

Environment

  • SmartStruxure
  • BACnet
  • ES
  • AS

Cause

The need to troubleshoot communications issues from device to device whether this is ES to AS or vice versa. The need to troubleshoot BACnet communications

Resolution

Network captures are beneficial in troubleshooting the following cases:

  1. Connection issues between SmartStruxure client and AS/ES.
    • If customers complain their client cannot connect to an AS/ES, a capture run from the client PC can be very useful. However, SmartStruxure uses TCP/HTTP and the payload is not easy to decode. There are no Wireshark decoders to help out, but the good news is that there is in communication logging built in to SmartStruxure that can replace the need for network captures. (See Error logs from the Enterprise Server for ES and see Error logs from an Automation Server and Enterprise Server for AS)
  2. Communication Status problems between servers and controllers (for example BACnet controllers).
    • The location of where the captures is taken can be very important. The best place to capture is at a switch directly connected to the controller. This may be difficult because it will require putting a “dumb” hub between the switch and the controller or finding a port mirroring switch.
  3. When you are not receiving BACnet alarms when expected.
  4. When you are not receiving COV notifications when expected
  5. When a trendlog is trending external point
  6. To evaluate the health of a network.
  7. ARP broadcast traffic can flood networks and can create connectivity problems on BACnet/IP networks. If this is the case then a customer can take action by segmenting their BMS to a VLAN.
  8. Performance problems on graphics where a large number of the point displayed are BACnet
  9. MS/TP bus performance is poor or MS/TP device is offline
  10. Using a USB RS-485 adapter can permit the capture of packets on an MS/TP bus. Wireshark can then be used to decode the packet captures. This can show token passing problems as well as traffic loads.

Also check out the BACnet-Capturing MS/TP Traffic Quick-Help video on the Exchange.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • 14916
  • losing
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore