Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Adding LoytecSrv (Loytec NIC) as a dependency to Enterprise Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Adding LoytecSrv (Loytec NIC) as a dependency to Enterprise Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • RobertAndriolo
    RobertAndriolo
  • RandyDavis
    RandyDavis
  • Cody_Failinger
    Cody_Failinger
  • Anonymous user
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2323 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Adding LoytecSrv (Loytec NIC) as a dependency to Enterprise Server

Picard Product_Support
‎2018-09-10 10:57 AM

Last Updated: Guinan RandyDavis Guinan ‎2025-04-22 06:40 AM

Issue

  • Configured Loytec LConfig application as a service but still do not get communication from the LonWorks Network.
  • Not able to get Service pin from LON devices connected with Loytec NIC from Enterprise Server

Product Line

EcoStruxure Building Operation

Environment

  • Enterprise Server 1.1
  • Loytec NIC852 (LConfig Tool)
  • Windows 7

Cause

  1. LConfig tool version is too old.
  2. The LConfig tool, even if set to start as a service, also still needs to start before the Enterprise Server (ES), otherwise the Enterprise Server fails to establish its connection with the LonWorks interface. For information on how to set LConfig to run as a service refer to Not able to get Service pin from LON devices connected with Loytec NIC from ES.

Resolution

To rectify the cause 1, click here to verify if the LConfig version is the most recent one. If not please download the most recent NIC - LOYTEC Network Interface Software.

To rectify the cause 2, you must set the Loytec (LConfig) application service to be a dependency of the Enterprise Server (ES), to do this follow these instructions:

  1. Using RegEdit (or similar) edit the Registry Key: HKEY_LOCAL_MACHINE\SYSTEM\CurrentControlSet\services\StruxureWare 1.1 Enterprise Server

    NOTE: For SmartStruxure version 1.3 and above, go to path: HKEY_LOCAL_MACHINE\SYSTEM\CurrentControlSet\services\Building Operation 1.3 Enterprise Server
  2. Locate and edit the DependOnService string
  3. Add the text LoytecSrv (service name for the LConfig application).

  4. Close the editor and reboot the PC

Note: When running the LConfig as a service the LConfig Tool is not available from the System Tray and must be started from the program shortcut, located under Start > Programs> LOYTEC Network Interfaces> LConfig

As a quick visual check, to see if configured correctly, you can perform a LonWorks Device Discovery on your Enterprise Server, this will show the NIC which has been defined with a red box (see image below). If these are all blue then you will not be able to receive any communications from your devices. Also remember if using the Loytec LIP devices that these should be configured in Smart Mode.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (4)
  • Find more articles tagged with:
  • 7541
  • integration
  • sever
  • TreyBoothe25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.