Posted: 2021-06-29 12:51 AM . Last Modified: 2024-03-13 11:42 PM
I have a blade rack with 3 Smart-UPS 6000s with AP9619 Network Management Cards. I have one external server with a serial port that can be connected to only one of the 3 upses.
I would like them to power off and power on their loads simultaneously and I can't figure out how to make that happen. I have tried creating a Sync Group however this doesn't seem to work when one of the Grouped upses recieves a shutdown.restart command over the serial cable.
When I run a shutdown from the web interface I get all 3 upses powering off at the same time but the one that initiated the shutdown always powers on first.
Idealy I would like to have my setup so that I can send one ups a shutdown command and have the other 2 follow it. This way I can control my UPS cluster via a single serial cable. Since the nut snmp-ups driver does not support shutdown I am kind of stuck
Thanks
Tom Parker
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:51 AM . Last Modified: 2024-03-13 11:42 PM
I have a blade rack with 3 Smart-UPS 6000s with AP9619 Network Management Cards. I have one external server with a serial port that can be connected to only one of the 3 upses.
I would like them to power off and power on their loads simultaneously and I can't figure out how to make that happen. I have tried creating a Sync Group however this doesn't seem to work when one of the Grouped upses recieves a shutdown.restart command over the serial cable.
When I run a shutdown from the web interface I get all 3 upses powering off at the same time but the one that initiated the shutdown always powers on first.
Idealy I would like to have my setup so that I can send one ups a shutdown command and have the other 2 follow it. This way I can control my UPS cluster via a single serial cable. Since the nut snmp-ups driver does not support shutdown I am kind of stuck
Thanks
Tom Parker
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:51 AM . Last Modified: 2024-03-13 11:42 PM
I have a blade rack with 3 Smart-UPS 6000s with AP9619 Network Management Cards. I have one external server with a serial port that can be connected to only one of the 3 upses.
I would like them to power off and power on their loads simultaneously and I can't figure out how to make that happen. I have tried creating a Sync Group however this doesn't seem to work when one of the Grouped upses recieves a shutdown.restart command over the serial cable.
When I run a shutdown from the web interface I get all 3 upses powering off at the same time but the one that initiated the shutdown always powers on first.
Idealy I would like to have my setup so that I can send one ups a shutdown command and have the other 2 follow it. This way I can control my UPS cluster via a single serial cable. Since the nut snmp-ups driver does not support shutdown I am kind of stuck
Thanks
Tom Parker