DLA1500RMI2U Insufficient Runtime Available (3030 Event ID)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • DLA1500RMI2U Insufficient Runtime Available (3030 Event ID)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:51 AM . Last Modified: ‎2024-03-13 11:42 PM

0 Likes
3
834
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:51 AM . Last Modified: ‎2024-03-13 11:42 PM

DLA1500RMI2U Insufficient Runtime Available (3030 Event ID)

I am getting Insufficient Runtime Available (3030 Event ID) on one of our DLA1500RMI2U. The unit is 5.5 years old, never replaced batteries. Serial is A50441120216. Has a 8 minute runtime on a 37% Load, Battery at 100%. Am unsure if its ever been calibrated as in Powerchute it says Calibration cancelled. We get the runtime error about every 15 minutes

Any ideas? Should I run a calibration on the unit, if so what is the procedure when running a live server (poweredge 2800), tape backup off of it? Should I replace the batteries?

The other unit is same spec, it has 66 minute runtime at 20% load on 100% battery

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:52 AM . Last Modified: ‎2024-03-13 11:42 PM

0 Likes
0
835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:52 AM . Last Modified: ‎2024-03-13 11:42 PM

I am getting Insufficient Runtime Available (3030 Event ID) on one of our DLA1500RMI2U. The unit is 5.5 years old, never replaced batteries. Serial is A50441120216. Has a 8 minute runtime on a 37% Load, Battery at 100%. Am unsure if its ever been calibrated as in Powerchute it says Calibration cancelled. We get the runtime error about every 15 minutes

Any ideas? Should I run a calibration on the unit, if so what is the procedure when running a live server (poweredge 2800), tape backup off of it? Should I replace the batteries?

The other unit is same spec, it has 66 minute runtime at 20% load on 100% battery

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:51 AM . Last Modified: ‎2024-03-13 11:42 PM

0 Likes
0
835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:51 AM . Last Modified: ‎2024-03-13 11:42 PM

Still 8 minutes runtime, UPS load is at 37% and it is set to begin shutdown after 5 minutes on battery.

The errors come through in a pattern within the hour, e.g. 10:30, 10:46 and 10:56 and so on

If I do a runtime Calibration, can I safely do ths whilst live equipment is attached, so as not to cause disruption to the workplace?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:51 AM . Last Modified: ‎2024-03-13 11:42 PM

0 Likes
0
835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:51 AM . Last Modified: ‎2024-03-13 11:42 PM

I will plan in a calibration, out of business hours. How long does a calib take approximately? And do I need to attach a few monitors to it to provide a load (above 30%)?

BTW, we have some new messages that have a similar pattern, "battery discharged" and immediately after "Battery charge in range"

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:52 AM . Last Modified: ‎2024-03-13 11:42 PM

0 Likes
0
836
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:52 AM . Last Modified: ‎2024-03-13 11:42 PM

I am getting Insufficient Runtime Available (3030 Event ID) on one of our DLA1500RMI2U. The unit is 5.5 years old, never replaced batteries. Serial is A50441120216. Has a 8 minute runtime on a 37% Load, Battery at 100%. Am unsure if its ever been calibrated as in Powerchute it says Calibration cancelled. We get the runtime error about every 15 minutes

Any ideas? Should I run a calibration on the unit, if so what is the procedure when running a live server (poweredge 2800), tape backup off of it? Should I replace the batteries?

The other unit is same spec, it has 66 minute runtime at 20% load on 100% battery

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now