Posted: 2021-06-29 12:51 AM . Last Modified: 2024-03-13 11:42 PM
I am getting Insufficient Runtime Available (3030 Event ID) on one of our DLA1500RMI2U. The unit is 5.5 years old, never replaced batteries. Serial is A50441120216. Has a 8 minute runtime on a 37% Load, Battery at 100%. Am unsure if its ever been calibrated as in Powerchute it says Calibration cancelled. We get the runtime error about every 15 minutes
Any ideas? Should I run a calibration on the unit, if so what is the procedure when running a live server (poweredge 2800), tape backup off of it? Should I replace the batteries?
The other unit is same spec, it has 66 minute runtime at 20% load on 100% battery
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:52 AM . Last Modified: 2024-03-13 11:42 PM
I am getting Insufficient Runtime Available (3030 Event ID) on one of our DLA1500RMI2U. The unit is 5.5 years old, never replaced batteries. Serial is A50441120216. Has a 8 minute runtime on a 37% Load, Battery at 100%. Am unsure if its ever been calibrated as in Powerchute it says Calibration cancelled. We get the runtime error about every 15 minutes
Any ideas? Should I run a calibration on the unit, if so what is the procedure when running a live server (poweredge 2800), tape backup off of it? Should I replace the batteries?
The other unit is same spec, it has 66 minute runtime at 20% load on 100% battery
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:51 AM . Last Modified: 2024-03-13 11:42 PM
Still 8 minutes runtime, UPS load is at 37% and it is set to begin shutdown after 5 minutes on battery.
The errors come through in a pattern within the hour, e.g. 10:30, 10:46 and 10:56 and so on
If I do a runtime Calibration, can I safely do ths whilst live equipment is attached, so as not to cause disruption to the workplace?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:51 AM . Last Modified: 2024-03-13 11:42 PM
I will plan in a calibration, out of business hours. How long does a calib take approximately? And do I need to attach a few monitors to it to provide a load (above 30%)?
BTW, we have some new messages that have a similar pattern, "battery discharged" and immediately after "Battery charge in range"
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:52 AM . Last Modified: 2024-03-13 11:42 PM
I am getting Insufficient Runtime Available (3030 Event ID) on one of our DLA1500RMI2U. The unit is 5.5 years old, never replaced batteries. Serial is A50441120216. Has a 8 minute runtime on a 37% Load, Battery at 100%. Am unsure if its ever been calibrated as in Powerchute it says Calibration cancelled. We get the runtime error about every 15 minutes
Any ideas? Should I run a calibration on the unit, if so what is the procedure when running a live server (poweredge 2800), tape backup off of it? Should I replace the batteries?
The other unit is same spec, it has 66 minute runtime at 20% load on 100% battery
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.