SURT3000XL Won't Shut Off

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURT3000XL Won't Shut Off
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 12:51 AM . Last Modified: β€Ž2024-03-13 11:42 PM

0 Likes
3
643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:51 AM . Last Modified: β€Ž2024-03-13 11:42 PM

SURT3000XL Won't Shut Off

Hi, I have an SURT3000XL with Extended Battery Pack that I bought used (both). The ribbon that connects to the plastic APC interface board where all the LEDS are, was ripped off during shipping.
So I stripped the cable and soldered all 8 strands onto the board then connected the ribbon to the UPS. As soon as I did the fan came on, so the batteries must have had some charge left. I used to be able to turn the unit on and off normally using the buttons on the interface.

I connected the extended battery pack to the unit and connected them to mains for like 40 mins...and during this time the green battery LEDS ( the leds to the right-charging voltage percentage) kept rising till they reached 4 marks. I was happy, disconnected the UPS from the mains, turned the unit off, and called it a day.

Next day my friend comes and plugs the unit into the mains, he says that none of the buttons were working. The unit just turns on by itself, does the self test, and kept charging. When you press the OFF button instead of turning off it starts to show the orange battery LED as if I'm connecting a load to the UPS that's draining the battery. If you press and HOLD the off button, you get all red leds flashing/flickering (a very faint dimm flicker). It just won't turn off.

I built the RS-232 cable to have a look at what's going on, everything seems normal, no errors. I found out that one of the 4 batteries in the extended pack had a blown fuse (2 blown fuses on a PCB 500v 30Amp Fuse). So I disconnected the entire extended battery unit and put it aside. Using HyperTerminal I adjusted the battery packs from 2 to 1 and fully charged the two batteries that come with the UPS.
Took about 2.5-3 hours to reach 100%, Runtime= 300 minutes. Then I choose option no.2 (UPS Controls) then no. 4 in the menu (off the top of my head it was Start Runtime Calibration test or so) and left it overnight to do the test which I think it drains the batteries and recharges them..I had no loads on the UPS and it was connected to the mains all night.

Next day I came with the test done, and batteries 100%, runtime 300 mins, 0% power loads. So I hooked up 2 computers and a 12V battery charger to the UPS. the 12V charger was hooked to my car with the car's lights on/Blower/CD player...the car was drawing 27 amps @14VDC. This setup lasted for 33 minutes for batteries to drain to 1% and I started to get continuous beeps from the UPS. So I removed the 12V battery charger & I had another 20 minutes to run the 2 PCs. I then recharged the batteries again to 100%, Runtime=300mins.

So I suppose the UPS and batteries are healthy except that it won't turn OFF like it first used to....I double checked the ribbon cable, no adjacent pins were shorted, and ran a continuity test everything seemed fine.
I think it's the PCB of the UPS itself....Any hints, schematics, most common failure points on the PCB (relay, fuse..etc) would be MUCH appreciated.

Taking it to an APC dealer isn't an option as I'm from one of the so called 3rd world countries where the price of just one RBC44 costs more than the average citizen's annual income (due to crazy taxes/customs).
I'm an electrical engineer so I'll gladly take any risk and won't blame anyone one if 1 of the 2 huge electrolytic capacitors discharges into my face.

Sorry for the long post, and THANKS for having this GREAT forum.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 12:51 AM . Last Modified: β€Ž2024-03-13 11:42 PM

0 Likes
0
643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:51 AM . Last Modified: β€Ž2024-03-13 11:42 PM

Hi, I have an SURT3000XL with Extended Battery Pack that I bought used (both). The ribbon that connects to the plastic APC interface board where all the LEDS are, was ripped off during shipping.
So I stripped the cable and soldered all 8 strands onto the board then connected the ribbon to the UPS. As soon as I did the fan came on, so the batteries must have had some charge left. I used to be able to turn the unit on and off normally using the buttons on the interface.

I connected the extended battery pack to the unit and connected them to mains for like 40 mins...and during this time the green battery LEDS ( the leds to the right-charging voltage percentage) kept rising till they reached 4 marks. I was happy, disconnected the UPS from the mains, turned the unit off, and called it a day.

Next day my friend comes and plugs the unit into the mains, he says that none of the buttons were working. The unit just turns on by itself, does the self test, and kept charging. When you press the OFF button instead of turning off it starts to show the orange battery LED as if I'm connecting a load to the UPS that's draining the battery. If you press and HOLD the off button, you get all red leds flashing/flickering (a very faint dimm flicker). It just won't turn off.

I built the RS-232 cable to have a look at what's going on, everything seems normal, no errors. I found out that one of the 4 batteries in the extended pack had a blown fuse (2 blown fuses on a PCB 500v 30Amp Fuse). So I disconnected the entire extended battery unit and put it aside. Using HyperTerminal I adjusted the battery packs from 2 to 1 and fully charged the two batteries that come with the UPS.
Took about 2.5-3 hours to reach 100%, Runtime= 300 minutes. Then I choose option no.2 (UPS Controls) then no. 4 in the menu (off the top of my head it was Start Runtime Calibration test or so) and left it overnight to do the test which I think it drains the batteries and recharges them..I had no loads on the UPS and it was connected to the mains all night.

Next day I came with the test done, and batteries 100%, runtime 300 mins, 0% power loads. So I hooked up 2 computers and a 12V battery charger to the UPS. the 12V charger was hooked to my car with the car's lights on/Blower/CD player...the car was drawing 27 amps @14VDC. This setup lasted for 33 minutes for batteries to drain to 1% and I started to get continuous beeps from the UPS. So I removed the 12V battery charger & I had another 20 minutes to run the 2 PCs. I then recharged the batteries again to 100%, Runtime=300mins.

So I suppose the UPS and batteries are healthy except that it won't turn OFF like it first used to....I double checked the ribbon cable, no adjacent pins were shorted, and ran a continuity test everything seemed fine.
I think it's the PCB of the UPS itself....Any hints, schematics, most common failure points on the PCB (relay, fuse..etc) would be MUCH appreciated.

Taking it to an APC dealer isn't an option as I'm from one of the so called 3rd world countries where the price of just one RBC44 costs more than the average citizen's annual income (due to crazy taxes/customs).
I'm an electrical engineer so I'll gladly take any risk and won't blame anyone one if 1 of the 2 huge electrolytic capacitors discharges into my face.

Sorry for the long post, and THANKS for having this GREAT forum.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 12:51 AM . Last Modified: β€Ž2024-03-13 11:42 PM

0 Likes
0
643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:51 AM . Last Modified: β€Ž2024-03-13 11:42 PM

Thanks for your input guys! I'll tripple check on the cable and the 2 boards that it connects to from both sides. Will post my findings too πŸ™‚

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 12:51 AM . Last Modified: β€Ž2024-03-13 11:42 PM

0 Likes
0
643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:51 AM . Last Modified: β€Ž2024-03-13 11:42 PM

It's been a very busy week at the workshop and I finally had a chance to give some TLC to my newly acquired APC.
I checked the cable many times, for connectivity or open circuits, it seemed fine but my soldering looked ugly. I must've been in a hurry or too excited, so I re-soldered it properly. I then inspected the LED board itsefl.The schmidt trigger IC (I think it was CD10406-BCM) under a magnifying glass. It had grey cracks on 2 legs so I just aimed the hot airg gun at it and let solder flow evenly.

I connected the unit, and it worked suuuuuperb. Even if the unit didn't work at ALL, I was still happy to own it (the PCB, connectors, components....great engineering!) and especially after building the serial cable and getting access to the cool menus...it's ALIVE!!! Board or no board it was already working πŸ˜›

Now I would still like to purchase that ribbon cable and the plastic black APC box that covers the L.E.D. board. A part no. and source online would be great guys.
I also intend to repaint or maybe powder coat the unit to remove all scratches...I might sound crazy but this is how I am when I get attached to something.

Thank you ALL!!!

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 12:51 AM . Last Modified: β€Ž2024-03-13 11:42 PM

0 Likes
0
644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:51 AM . Last Modified: β€Ž2024-03-13 11:42 PM

Hi, I have an SURT3000XL with Extended Battery Pack that I bought used (both). The ribbon that connects to the plastic APC interface board where all the LEDS are, was ripped off during shipping.
So I stripped the cable and soldered all 8 strands onto the board then connected the ribbon to the UPS. As soon as I did the fan came on, so the batteries must have had some charge left. I used to be able to turn the unit on and off normally using the buttons on the interface.

I connected the extended battery pack to the unit and connected them to mains for like 40 mins...and during this time the green battery LEDS ( the leds to the right-charging voltage percentage) kept rising till they reached 4 marks. I was happy, disconnected the UPS from the mains, turned the unit off, and called it a day.

Next day my friend comes and plugs the unit into the mains, he says that none of the buttons were working. The unit just turns on by itself, does the self test, and kept charging. When you press the OFF button instead of turning off it starts to show the orange battery LED as if I'm connecting a load to the UPS that's draining the battery. If you press and HOLD the off button, you get all red leds flashing/flickering (a very faint dimm flicker). It just won't turn off.

I built the RS-232 cable to have a look at what's going on, everything seems normal, no errors. I found out that one of the 4 batteries in the extended pack had a blown fuse (2 blown fuses on a PCB 500v 30Amp Fuse). So I disconnected the entire extended battery unit and put it aside. Using HyperTerminal I adjusted the battery packs from 2 to 1 and fully charged the two batteries that come with the UPS.
Took about 2.5-3 hours to reach 100%, Runtime= 300 minutes. Then I choose option no.2 (UPS Controls) then no. 4 in the menu (off the top of my head it was Start Runtime Calibration test or so) and left it overnight to do the test which I think it drains the batteries and recharges them..I had no loads on the UPS and it was connected to the mains all night.

Next day I came with the test done, and batteries 100%, runtime 300 mins, 0% power loads. So I hooked up 2 computers and a 12V battery charger to the UPS. the 12V charger was hooked to my car with the car's lights on/Blower/CD player...the car was drawing 27 amps @14VDC. This setup lasted for 33 minutes for batteries to drain to 1% and I started to get continuous beeps from the UPS. So I removed the 12V battery charger & I had another 20 minutes to run the 2 PCs. I then recharged the batteries again to 100%, Runtime=300mins.

So I suppose the UPS and batteries are healthy except that it won't turn OFF like it first used to....I double checked the ribbon cable, no adjacent pins were shorted, and ran a continuity test everything seemed fine.
I think it's the PCB of the UPS itself....Any hints, schematics, most common failure points on the PCB (relay, fuse..etc) would be MUCH appreciated.

Taking it to an APC dealer isn't an option as I'm from one of the so called 3rd world countries where the price of just one RBC44 costs more than the average citizen's annual income (due to crazy taxes/customs).
I'm an electrical engineer so I'll gladly take any risk and won't blame anyone one if 1 of the 2 huge electrolytic capacitors discharges into my face.

Sorry for the long post, and THANKS for having this GREAT forum.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of