Symmetra LX 16kVA - XR FAULT ERROR?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra LX 16kVA - XR FAULT ERROR?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-07 11:15 PM . Last Modified: ‎2024-03-01 12:05 AM

0 Likes
2
1523
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:15 PM . Last Modified: ‎2024-03-01 12:05 AM

Symmetra LX 16kVA - XR FAULT ERROR?

UPS is running on 4 battery modules plus XR with 3 battery modules, suddenly UPS started to beep with notification E7 / 02  and communication software report said; XR FRAME FAULT

despite in properties of main battery and XR batteries seems all  in perfect condition with no single error ?!?!

USP works fine, runtime is still like before, all the batteries (changed a year ago, brand new original) are in perfect condition, (measured voltage and capacity inside the each module (pack of 10 batteries per module), input and output voltages are fine....all the tests are passing OK, nothing really changed but only this beep sound and E7 error is showing...

i have tried to reseat the RJ11 comm plug on both sides, all seems fine, but erorr is beeping for XR FRAME

that happened simple like out of blue.....it was all working fine and suddenly we heard beep signal....i am confused....

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 11:15 PM . Last Modified: ‎2024-03-01 12:05 AM

0 Likes
0
1522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:15 PM . Last Modified: ‎2024-03-01 12:05 AM

I have some 20-year-old Matrix units (with modern batteries) and I've had to replace the RJ cables a couple times (actually, I just cut off the ends and crimp new connectors on). Usually just unplugging the cables and blowing the dust out of the jack and wiping the plugs with a dry paper towel will clear things up for a while.

The RJ just carries information about the number of battery packs and battery health - the actual battery power goes though the heavy Anderson connector. As long as the UPS relies on the battery voltage to determine when to shut down due to low battery, the actual runtime isn't affected by problems with the RJ cables. The displayed runtime, of course, will be inaccurate and you get alarms about communication faults and/or changing numbers of battery packs.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:15 PM . Last Modified: ‎2024-03-01 12:05 AM

0 Likes
0
1522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:15 PM . Last Modified: ‎2024-03-01 12:05 AM

Hello Vlad,

An E7 on an LX XR frame indicates a communication problem. This could either be the RJ9 communication cable, the XR COM card on the XR frame, or any module in the main unit that could be failing and causing COM problems.

If it was the later it would be evident as you would be getting other types of faults on the main unit and/or the powerview display would be acting up. But that does not sound like your case.

The other 2 possible scenarios should be investigated. The RJ9 communication cable is 4 pin straight through cable. You could try swapping that out if you have another. If that is not the issue (I very rarely, if ever, see the problem originating from the cable) then the XR COM card would be suspect. This card is the SYAFSU16.

If I were you I would place the LX into maintenance bypass using the bypass switch on the front of the unit. Then I would go around back of the UPS and toggle the System Enable switch. Flip it down and wait a few seconds and then flip it back up. As long as you are in maintenance bypass and there are no faults on the LX itself (not the XR frame) you can safely perform this task without risk of dropping your load. This will essentially refresh the COM bus on the LX and might clear the fault. If the fault does not clear or returns you would need to look at replacing the SYAFSU16.

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 11:15 PM . Last Modified: ‎2024-03-01 12:05 AM

0 Likes
0
1523
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:15 PM . Last Modified: ‎2024-03-01 12:05 AM

I have some 20-year-old Matrix units (with modern batteries) and I've had to replace the RJ cables a couple times (actually, I just cut off the ends and crimp new connectors on). Usually just unplugging the cables and blowing the dust out of the jack and wiping the plugs with a dry paper towel will clear things up for a while.

The RJ just carries information about the number of battery packs and battery health - the actual battery power goes though the heavy Anderson connector. As long as the UPS relies on the battery voltage to determine when to shut down due to low battery, the actual runtime isn't affected by problems with the RJ cables. The displayed runtime, of course, will be inaccurate and you get alarms about communication faults and/or changing numbers of battery packs.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of