Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Additional time with multiple battery packs

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Additional time with multiple battery packs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-07 11:15 PM . Last Modified: ‎2024-03-01 12:05 AM

0 Likes
2
688
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:15 PM . Last Modified: ‎2024-03-01 12:05 AM

Additional time with multiple battery packs

I have an SMX1000 that has a SMX48RMBP2U attached to it.  When looking at the UPS through a web browser, I have 18 hrs + of run time.  If I install an additional battery pack, the run time vlaue does not increase.  The software does see both battery packs installed.  I have done runtime calibrations and battery self tests, the value does not update to the higher hourly projected time of 32 hrs.   

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-07 11:15 PM . Last Modified: ‎2024-03-01 12:05 AM

0 Likes
0
687
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:15 PM . Last Modified: ‎2024-03-01 12:05 AM

With a SMX1000 and one SMX48RMBP2U, with a 100% charge, I typicaly see 18 hours 20 mins run time with no load (My unit will rarely run over 20% load when applied)  When I do add multiple SMX48RMBP2U battery packs, the run time value does not change. (this is my concern)  My units will run appoximatly 1 Hour and 45 mins if unplugged from commercial power with a 500W load during runtime calibration, that is in line with the run times APC calls out.  My concern is the run time reading in the browser window or from the front panel does not reflect the amount of additional battery packs in place. I am under the impression that this is a software set value from APC and it will not increase.     

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:15 PM . Last Modified: ‎2024-03-01 12:05 AM

0 Likes
0
687
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:15 PM . Last Modified: ‎2024-03-01 12:05 AM

What is the exact figure it shows? 18 hours, how many minutes? I was thinking, some of our older UPSs couldn't display past a certain value (even though it will run for the right amount of time) but I am not sure about these new ones.

How much load % is on your UPS? The 32 hour figure I saw if you have 50W on the UPS. Anytime you do runtime calibrations, for them to be worthwhile, you'll want at least 30% load not to fluctuate more than +/- 5% typically.

Lastly, does the value change if you let the UPS run on battery for a bit - either by pulling the plug or when you did do the calibration?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 11:15 PM . Last Modified: ‎2024-03-01 12:05 AM

0 Likes
0
688
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:15 PM . Last Modified: ‎2024-03-01 12:05 AM

With a SMX1000 and one SMX48RMBP2U, with a 100% charge, I typicaly see 18 hours 20 mins run time with no load (My unit will rarely run over 20% load when applied)  When I do add multiple SMX48RMBP2U battery packs, the run time value does not change. (this is my concern)  My units will run appoximatly 1 Hour and 45 mins if unplugged from commercial power with a 500W load during runtime calibration, that is in line with the run times APC calls out.  My concern is the run time reading in the browser window or from the front panel does not reflect the amount of additional battery packs in place. I am under the impression that this is a software set value from APC and it will not increase.     

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of