Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

Smart UPS 420 fails with system overload repeatable on saturday afternoon between 3 and 4 a clock pm

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS 420 fails with system overload repeatable on saturday afternoon between 3 and 4 a clock pm
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
ecaroh_apc
ecaroh_apc
Cadet

Posted: ‎2021-06-30 11:07 PM

0 Likes
0
117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 11:07 PM

Smart UPS 420 fails with system overload repeatable on saturday afternoon between 3 and 4 a clock pm

This was originally posted on APC forums on 11/23/2015


I have an SMART UPS 420 with batteries one year old. There should be no battery overload, cause besides a modem and a router only one small server is attached. APCUPSD says it has 33 % UPS Load, 100 % Battery capacity and 32 mins run time remaining.

The UPS suddenly fails supplying power. The server and the modem are powered of. The UPS has an ongoing beep and the system overload LED is on. I have to switch the UPS on again.

The surprising fact is, that this happened round about 5 times in the last year always on a saturday afternoon between 3 and 4 pm. There are no hints from the apcupsd event logs. I have no clue where to start, cause i can not imagine an overload causing the situation. Especially when there should be not more load on the weekend. The monitoring of the server has no hint of extra cpu load at this time. And there has been more load on it while it worked without outage. To reduce it i bought a second UPS and divided system load between them. 

Below the output of apcupsd running on linux with serial cable. Does anybody have ideas of a saturday afternoon overload? The last outage happend apr. at 4:00 pm 1 and a half hour before the last log line on 2015-11-21 17:23:38 with message unknown startup succeeded when i bring back the ups online again.

Just a guess; can apcupsd on linux shut down the power via the serial cable? Then it maybe a fault on apcupsd side?

This are samples of "unknown startup succeeded" - always saturday after a shutdown/overload where i started the ups again:

  1 2015-11-21 17:23:38 +0100

  2 2015-10-24 16:56:27 +0200

  3 2015-08-29 17:39:41 +0200

  4 2015-07-18 09:20:09 +0200

  5 2015-07-04 11:22:44 +0200

  6 2015-03-21 13:18:41 +0100

  7 2015-01-17 15:28:47 +0100

  8 2014-12-06 15:20:39 +0100

  9 2014-11-15 16:47:59 +0100

10 2014-11-08 17:28:59 +0100

11 2014-10-11 17:20:36 +0200

Monitoring: of-srv-ipf-1
 UPS Model: Smart-UPS 420   
  UPS Name: UPS_IDEN
   APCUPSD: Version 3.14.10
    Status: ONLINE 
Last UPS Self Test: NO
Last Test Date: Not found
Utility Voltage: 233.2 VAC
   Line Minimum: 231.8 VAC
   Line Maximum: 233.2 VAC
    Output Freq: 50.0 Hz

2015-11-21 17:23:38 +0100 apcupsd 3.14.10 (13 September 2011) unknown startup succeeded
2015-10-24 16:56:27 +0200 apcupsd 3.14.10 (13 September 2011) unknown startup succeeded
2015-09-17 15:58:20 +0200 Power is back. UPS running on mains.
2015-09-17 15:58:18 +0200 Power failure.
2015-08-29 17:39:41 +0200 apcupsd 3.14.10 (13 September 2011) unknown startup succeeded
2015-08-29 16:31:06 +0200 apcupsd shutdown succeeded
2015-08-29 16:31:06 +0200 apcupsd exiting, signal 15
2015-08-29 14:52:36 +0200 apcupsd 3.14.10 (13 September 2011) unknown startup succeeded
2015-08-29 14:49:06 +0200 apcupsd shutdown succeeded
2015-08-29 14:49:06 +0200 apcupsd exiting, signal 15
2015-08-25 15:39:32 +0200 Power is back. UPS running on mains.
2015-08-25 15:39:30 +0200 Power failure.
2015-08-15 16:22:47 +0200 UPS Self Test completed: Battery OK
2015-08-15 16:22:39 +0200 UPS Self Test switch to battery.
2015-08-01 16:22:13 +0200 UPS Self Test completed: Battery OK
2015-08-01 16:22:06 +0200 UPS Self Test switch to battery.
2015-07-24 14:44:00 +0200 apcupsd 3.14.10 (13 September 2011) unknown startup succeeded
2015-07-24 14:39:54 +0200 apcupsd shutdown succeeded
2015-07-24 14:39:54 +0200 apcupsd exiting, signal 15
2015-07-18 16:22:30 +0200 UPS Self Test completed: Battery OK
2015-07-18 16:22:27 +0200 UPS Self Test switch to battery.
2015-07-18 09:20:09 +0200 apcupsd 3.14.10 (13 September 2011) unknown startup succeeded
2015-07-18 09:16:43 +0200 apcupsd shutdown succeeded
2015-07-18 09:16:43 +0200 apcupsd exiting, signal 15
2015-07-04 11:22:44 +0200 apcupsd 3.14.10 (13 September 2011) unknown startup succeeded
2015-07-04 11:19:17 +0200 apcupsd shutdown succeeded
2015-07-04 11:19:17 +0200 apcupsd exiting, signal 15
2015-06-01 03:02:31 +0200 Power is back. UPS running on mains.
2015-06-01 03:02:29 +0200 Power failure.
2015-06-01 03:01:47 +0200 Power is back. UPS running on mains.
2015-06-01 03:01:45 +0200 Power failure.
2015-04-01 17:24:35 +0200 apcupsd 3.14.10 (13 September 2011) unknown startup succeeded
2015-04-01 17:21:03 +0200 apcupsd shutdown succeeded
2015-04-01 17:21:03 +0200 apcupsd exiting, signal 15
2015-03-21 13:18:41 +0100 apcupsd 3.14.10 (13 September 2011) unknown startup succeeded
2015-03-21 13:15:17 +0100 apcupsd shutdown succeeded
2015-03-21 13:15:17 +0100 apcupsd exiting, signal 15
2015-01-28 11:11:27 +0100 Power is back. UPS running on mains.
2015-01-28 11:11:26 +0100 Power failure.
2015-01-25 12:40:48 +0100 apcupsd 3.14.10 (13 September 2011) unknown startup succeeded
2015-01-25 12:37:30 +0100 apcupsd shutdown succeeded
2015-01-25 12:37:30 +0100 apcupsd exiting, signal 15
2015-01-17 15:28:47 +0100 apcupsd 3.14.10 (13 September 2011) unknown startup succeeded
2015-01-14 19:23:09 +0100 apcupsd 3.14.10 (13 September 2011) unknown startup succeeded
2015-01-14 19:19:46 +0100 apcupsd shutdown succeeded
2015-01-14 19:19:46 +0100 apcupsd exiting, signal 15
2014-12-20 15:17:33 +0100 UPS Self Test completed: Battery OK
2014-12-20 15:17:26 +0100 UPS Self Test switch to battery.
2014-12-06 15:20:39 +0100 apcupsd 3.14.10 (13 September 2011) unknown startup succeeded
2014-11-15 16:47:59 +0100 apcupsd 3.14.10 (13 September 2011) unknown startup succeeded

output of apcupsd.conf without comments: 

UPSCABLE smart

UPSTYPE apcsmart

DEVICE /dev/ttyS0

LOCKFILE /var/lock

SCRIPTDIR /etc/apcupsd

PWRFAILDIR /etc/apcupsd

NOLOGINDIR /etc

ONBATTERYDELAY 6

BATTERYLEVEL 5

MINUTES 3

TIMEOUT 0

ANNOY 300

ANNOYDELAY 60

NOLOGON disable

KILLDELAY 0

NETSERVER on

NISIP 0.0.0.0

NISPORT 3551

EVENTSFILE /var/log/apcupsd.events

EVENTSFILEMAX 10

UPSCLASS standalone

UPSMODE disable

STATTIME 0

STATFILE /var/log/apcupsd.status

LOGSTATS off

DATATIME 0

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc