Ask our Experts
Didn't find what you are looking for? Ask our experts!
Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-30 11:07 PM . Last Modified: 2024-03-06 03:24 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 11:07 PM . Last Modified: 2024-03-06 03:24 AM
Trying to troubleshoot issue with repeated instances of alert "conpensating for high input voltage". Looking at Data log, I see that those alerts seem to come at a time when the Iout value goes from 1.33 to 1.50. I don't know what this means
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 11:07 PM . Last Modified: 2024-03-06 03:24 AM
Iout is the output current, or, the current drawn by the load. Things like fans and light bulbs draw more current when the voltage is higher, so it could just be a consequence of compensation. On the other hand, in areas with poor wiring or where the circuit is at capacity, drawing more current causes the voltage to drop which causes the UPS to boost. For example when my laser printer turns on, it draws a lot of power and my lights flicker because of the voltage drop.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 11:07 PM . Last Modified: 2024-03-06 03:24 AM
Iout is the output current, or, the current drawn by the load. Things like fans and light bulbs draw more current when the voltage is higher, so it could just be a consequence of compensation. On the other hand, in areas with poor wiring or where the circuit is at capacity, drawing more current causes the voltage to drop which causes the UPS to boost. For example when my laser printer turns on, it draws a lot of power and my lights flicker because of the voltage drop.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 11:07 PM . Last Modified: 2024-03-06 03:24 AM
To add one minor note, current is measured in amps so the values you see in the IOut column in the data log are 1.XX amps.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.