How to calibrate after Battery Replacement

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How to calibrate after Battery Replacement
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 11:07 PM . Last Modified: ‎2024-03-06 03:24 AM

0 Likes
4
12500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:07 PM . Last Modified: ‎2024-03-06 03:24 AM

How to calibrate after Battery Replacement

Hi,

    I have an SUA1500i model APC UPS Purchased on 11th January 2013. In October 2015 it's backup time

reduced to 5 minutes. Upon inspection one of the internal battery was found to be down. Then I replaced

the Batteries with Amaron Quanta 12 V 18 AH Batteries( 2 No.s). Now next day after replacement suddenly

there was a Beep sound and the Battery Charge LED is showing the lowest charge level. Then the APC Dealer who 

replaced the Battery says it has to be Calibrated and for that 9-port is required. How to calibrate and what is this port?

Is USB Port enough ? SUA1500i model UPS is having one serial port and one USB port. Please help. Thanks in advance.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery
  • replacement
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 11:08 PM . Last Modified: ‎2024-03-06 03:24 AM

0 Likes
0
12503
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:08 PM . Last Modified: ‎2024-03-06 03:24 AM

Hi Stuart,

             Thanks a lot for the fast, detailed response. Sure it did help. Can I use a USB Cable instead of the serial cable?

Regards

See Answer In Context

  • Tags:
  • battery
  • calibration
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-30 11:08 PM . Last Modified: ‎2024-03-06 03:24 AM

0 Likes
0
12503
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:08 PM . Last Modified: ‎2024-03-06 03:24 AM

Hi Jayan,

First you could try a manual battery calibration.

1. Charge the batteries fro atleast 8 hours

2. Stop the PowerChute plus software from running and disconnect
the serial cable.

3. There must be at least a 30% load attached to the UPS during
this procedure, but the process will cause the UPS to shut off and cut power to
its outlets. Therefore, attach a non-critical load to the UPS and then force
the UPS on battery by disconnecting it from utility power. Allow the unit to
run on battery until it turns off completely. Make sure at least a 30% load is
present!

4. Plug the UPS back into the wall outlet and allow it to recharge (it
will recharge more quickly turned off and with no load present). Once the unit
has recharged, the ""runtime remaining"" calculation should be more accurate.

Hopefully this helps

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 11:08 PM . Last Modified: ‎2024-03-06 03:24 AM

0 Likes
0
12504
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:08 PM . Last Modified: ‎2024-03-06 03:24 AM

Hi Stuart,

             Thanks a lot for the fast, detailed response. Sure it did help. Can I use a USB Cable instead of the serial cable?

Regards

  • Tags:
  • battery
  • calibration
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:08 PM . Last Modified: ‎2024-03-06 03:24 AM

0 Likes
0
12503
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:08 PM . Last Modified: ‎2024-03-06 03:24 AM

Jayan,

If you are following the procedure Stuart recommended you do not need either cable. If you are running PowerChute depending on the version you can use either USB or Serial.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 11:08 PM . Last Modified: ‎2024-03-06 03:23 AM

0 Likes
0
12503
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:08 PM . Last Modified: ‎2024-03-06 03:23 AM

Hi Bill,

           Thanks a lot. Now everything is clear.  Here some unprofessional people were confusing by giving

            wrong information by saying 9-port is required for running calibration etc.

            I'm so glad that I have joined the A P C Forum. Thanks once again Bill and Stuart.

Regards,

Jayan

  • Tags:
  • battery
  • calibration
  • smartups
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore