SURTD3000RMXLT3U with L14-30 to L6-30 adapter
Hi,
My electricians installed a NEMA L14-30R receptacle running at 208V for use with an APC SURTD5000RMXLP3U UPS. However, since then, my power requirements have dropped drastically. Now I can easily get by with the APC SURTD3000RMXLT3U. (All of the devices in the rack can run at 208V, so I don't need the transformer, either.)
Can I safely use the SURTD3000RMXLT3U with the L14-30R circuit and an L14-30P to L6-30R adapter? I would assume so, as the adapters are easy to find and presumably the SURTD3000RMXLT3U will just not use the neutral wire, but better safe than sorry.
thanks!
- Labels:
-
Smart-UPS & Symmetra LX | RM
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:16 AM . Last Modified: 2024-03-12 04:36 AM
I also believe it will be fine but local code probably has the final say. I would assume the electrician could verify for you as well that there is no issue with doing this based on your location.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:16 AM . Last Modified: 2024-03-12 04:36 AM
I also believe it will be fine but local code probably has the final say. I would assume the electrician could verify for you as well that there is no issue with doing this based on your location.
Link copied. Please paste this link to share this article on your social media post.