OS doesn't shutdown with the OS shutdown delay timing

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • OS doesn't shutdown with the OS shutdown delay timing
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 09:04 PM . Last Modified: โ€Ž2024-03-15 01:31 AM

0 Likes
9
803
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 09:04 PM . Last Modified: โ€Ž2024-03-15 01:31 AM

OS doesn't shutdown with the OS shutdown delay timing

Hi,

I have Powerchute Business v8 installed on our 2003 server. I have the runtime remaining threshold set to 5 mins and the OS shutdown delay set to 3 mins. I tested the configuration by unpluging the power source on the UPS (smartups 700). The server did give me notification once it reached the 5 mins threshold. However the server shut itself down 1 min after the runtime remaining threshold reached. I though the server would shutdown itself until 3 mins passed the threshold. Did I miss something here? Also, can someone tell me if the low battery signal timing (currently set to 2 mins) has any impact to the above configuration?

Thanks

Message was edited by: uminds

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 09:05 PM . Last Modified: โ€Ž2024-03-15 01:31 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 09:05 PM . Last Modified: โ€Ž2024-03-15 01:31 AM

Thank you very much for your help.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-28 09:04 PM . Last Modified: โ€Ž2024-03-15 01:31 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 09:04 PM . Last Modified: โ€Ž2024-03-15 01:31 AM

Hello,

Could you tell us all of the events you have Shutdown scheduled for and what the time frames are?

It sounds likely that you have a couple of different events set for shutdown and they may be overlapping, triggering before the one you really want to.

Take a look at the actions page and anything that has the little green dot under the shutdown column.

Also what are the following set to:

Time Required For Shutdown Sequence


Let us know ๐Ÿ™‚

Message was edited by: syn2083

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 09:04 PM . Last Modified: โ€Ž2024-03-15 01:31 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 09:04 PM . Last Modified: โ€Ž2024-03-15 01:31 AM

I only enabled shutdown for low batttery condition. As I mentioned, the runtime remaining is set to 5 mins (this is the time required for shutdown sequence)

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-28 09:04 PM . Last Modified: โ€Ž2024-03-15 01:31 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 09:04 PM . Last Modified: โ€Ž2024-03-15 01:31 AM

Ok, I gotcha.

The delay that your talking about is not quite what your thinking it is, here is it's description:

OS Shutdown Delay:
The maximum time required for OS shutdown after the configured command file has completed. After this delay, the UPS will turn off its output, turning off power to the protected system.

So basically the delay is stating that this is how long the OS will take to shutdown, when this is complete I (the UPS) can now turn off. This is not a delay for how long the unit will wait before shutting the OS down.

Hope this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 09:04 PM . Last Modified: โ€Ž2024-03-15 01:31 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 09:04 PM . Last Modified: โ€Ž2024-03-15 01:31 AM

I just tested the configuration. It looks like I have to specify time duration for the shutdown script to executre. By default, the command file execution duration is set to 0 and it didn't seem to run if I leave it as default.

I still don't see how the OS shutdown delay comes into place in this situation as the machine shutdown 1 min (this is the time I specified for the command file execution duration) after the remaining time threshold reached.

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-28 09:05 PM . Last Modified: โ€Ž2024-03-15 01:31 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 09:05 PM . Last Modified: โ€Ž2024-03-15 01:31 AM

The shutdown delay will begin after the script timer, so the timeline is:

1, time for total shutdown
2, command file timer
3, OS delay time (which is simply how long the OS takes to shutdown)
4, ups turn off after OS delay

So the time remaining triggers, the command runs at whatever time interval you set, the OS delay time you set kicks in after the command file, then the ups waits to shutdown for the amount of time that was set in OS delay.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 09:05 PM . Last Modified: โ€Ž2024-03-15 01:31 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 09:05 PM . Last Modified: โ€Ž2024-03-15 01:31 AM

Thanks a lot, it starts making sense now.

One more question, what does time low battery signal timing for? Do I have to worry about it at all?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-28 09:05 PM . Last Modified: โ€Ž2024-03-15 01:31 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 09:05 PM . Last Modified: โ€Ž2024-03-15 01:31 AM

In this instance, no you should be fine. Otherwise it is the time that the unit will mark when the low battery begins its countdown, so if you had your settings based off of low battery itself it would be important, but you arent so you should be fine with the setup your using.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-28 09:05 PM . Last Modified: โ€Ž2024-03-15 01:31 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 09:05 PM . Last Modified: โ€Ž2024-03-15 01:31 AM

Anytime, have a great day!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 09:05 PM . Last Modified: โ€Ž2024-03-15 01:31 AM

0 Likes
0
805
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 09:05 PM . Last Modified: โ€Ž2024-03-15 01:31 AM

Thank you very much for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of