Battery Runtime Incorrect

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Battery Runtime Incorrect
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:05 PM . Last Modified: β€Ž2024-03-15 01:31 AM

0 Likes
7
2031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:05 PM . Last Modified: β€Ž2024-03-15 01:31 AM

Battery Runtime Incorrect

Hello Everyone,

I recently replaced my Smart-UPS RT 3000 XL w/ two external batteries and an APC9619 Management card because it was at the end of its lease. Instead of purchasing two external batteries we decided to purchase one external battery.

When I log onto the AP9619 in the replaced UPS system it reports a load of 40% and a battery uptime of 43minutes. The battery uptime value is incorrect and I believe it should be reporting around 2 hours. We ran some tests (such as calibration and battery test) and the value does not change. We confirmed the external battery was connected properly and the management card reflects 1 external battery connected.

When we cut power to the UPS and log onto the management window we notice the battery uptime value changes to nearly 2 hours. Could you please advise how to fix the battery uptime value so it reflects the proper value on my reports?

Thank you,
D

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:05 PM . Last Modified: β€Ž2024-03-15 01:31 AM

0 Likes
0
2028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:05 PM . Last Modified: β€Ž2024-03-15 01:31 AM

Hello, I have the same situation, the difference is that we already configure the ups to two banks, the internal + 1 external = 2, the model of the ups is: Smart-UPS RT 3000 RM XL, when we perform the runtime calibration, the The battery lasts 3 hours and a few minutes, but then when the batteries are 100% charged the Runtime Remaining is only 50-60 minutes. We have already turned it off, disconnected all the charges and turned it on again and the Runtime Remaining continues in 50-60 minutes.

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 09:05 PM . Last Modified: β€Ž2024-03-15 01:31 AM

0 Likes
0
2028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:05 PM . Last Modified: β€Ž2024-03-15 01:31 AM

hi derek,

can you confirm the model on this UPS via the sticker on the unit?

Is it an SURT3000XLT, SURTA3000XL, or a SURTD3000XLT?

If it is one of the first two mentioned, we can reset the battery constants via Hyperterminal or some terminal program - which I can walk you through doing that via email or private message. if its an SURTD3000XLT, we will need to proceed in a different direction. The SURTD3000XLTs are fairly new - only around about a little over a year I think.

Let me know and we'll go from there.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:05 PM . Last Modified: β€Ž2024-03-15 01:31 AM

0 Likes
0
2028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:05 PM . Last Modified: β€Ž2024-03-15 01:31 AM

Hi Angela,

As always- thank you for your prompt assistance πŸ™‚

The devices are 2 weeks old. Unfortunately I am unable to find the exact model# on the device via the web interface or the hyperterminal connection, however, I have the serial number if that helps?

I've sent you some information via private message.

Thanks,
D

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:05 PM . Last Modified: β€Ž2024-03-15 01:31 AM

0 Likes
0
2028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:05 PM . Last Modified: β€Ž2024-03-15 01:31 AM

Hi Angela,

I responded to your PM

Thank you,
D

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 09:05 PM . Last Modified: β€Ž2024-03-15 01:31 AM

0 Likes
0
2028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:05 PM . Last Modified: β€Ž2024-03-15 01:31 AM

Hey there, just something I noticed in your post, if your using an external pack, the count in the unit should reflect the following, per user manual:

Enter the number of battery packs, including the internal battery pack
(Number of packs: 1= internal battery module, 2 = 1 SURT192XLBP, 3 = 2
SURT192XLBP, etc.).

so in your case, your batt pack # should be set to 2.

This might also have something to do with your runtime reflecting improperly. Hope this helps πŸ™‚

Message was edited by: syn2083

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:05 PM . Last Modified: β€Ž2024-03-15 01:31 AM

0 Likes
0
2028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:05 PM . Last Modified: β€Ž2024-03-15 01:31 AM

Hi Tim,

Thank you for your note. The AP9619 web interface reports 1 external battery (rather than 2). When I changed the value to 2 the system reports 3 1/2 hrs uptime.

Thank you,
D

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 09:05 PM . Last Modified: β€Ž2024-03-15 01:31 AM

0 Likes
0
2028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:05 PM . Last Modified: β€Ž2024-03-15 01:31 AM

Excellent, glad to help, have a nice day πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:05 PM . Last Modified: β€Ž2024-03-15 01:31 AM

0 Likes
0
2029
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:05 PM . Last Modified: β€Ž2024-03-15 01:31 AM

Hello, I have the same situation, the difference is that we already configure the ups to two banks, the internal + 1 external = 2, the model of the ups is: Smart-UPS RT 3000 RM XL, when we perform the runtime calibration, the The battery lasts 3 hours and a few minutes, but then when the batteries are 100% charged the Runtime Remaining is only 50-60 minutes. We have already turned it off, disconnected all the charges and turned it on again and the Runtime Remaining continues in 50-60 minutes.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of