Hello!
In project we have 2 rooms, each has one InRow, ACRC301S and ACRC502, and one chiller Uniflair ISAF 1221A. We want to integrate OMI (Optimized Management Interface). Can it be done with this exact models?
p.s. Where we can find installation guide, manuals and etc.?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:08 AM . Last Modified: 2024-03-18 12:04 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:08 AM . Last Modified: 2024-03-18 12:04 AM
Hello
looking for OIDs of ACRC301S
with current version of MIB I'm not able to figure out the OIDs for this AIRCO model.
any chance you can help here?
thank you
Petr
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:08 AM . Last Modified: 2024-03-18 12:04 AM
Hello.
The ACRC301S and the ACRC502 are able to communicate over modbus RTU or be configured to send SNMP traps to a management platform. As long as the OMI can communicate through these protocols, these units can communicate with the OMI. For the chiller, these can communicate over RS485, LonWorks, BACnet or TCP/IP depending on the accessory cards that are purchased with the unit. I have copied some links to our websites below where you can find for documentation on the units. For the Chiller, if you have more questions I recommend you to give a call to your country's support line, as they can give you the options available in your country.
Thank you
ACRC301S
ACRC502
Buy InRow RC, 600mm, Chilled Water, 380-415V, 50Hz - Technical Specifications and Information | APC
Chiller
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:08 AM . Last Modified: 2024-03-18 12:04 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:08 AM . Last Modified: 2024-03-18 12:04 AM
Hello
looking for OIDs of ACRC301S
with current version of MIB I'm not able to figure out the OIDs for this AIRCO model.
any chance you can help here?
thank you
Petr