Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-28 08:08 AM . Last Modified: 2024-03-18 12:04 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:08 AM . Last Modified: 2024-03-18 12:04 AM
We have a APC MasterSwith AP7900 that shows a status of "Power Supply 2 Alarm" within the web interface. Do these units actually have 2 power supplies? Does anyone know the severity of this error and what needs to be done to resolve it? It just seems like an odd error since there is only 1 power cable from the unit and it does not seem to have multiple power supplies.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:08 AM . Last Modified: 2024-03-18 12:04 AM
Hello,
This refers to one of the two internal DC power supplies. Switched Rack PDUs contain a primary and a secondary power supply. (Metered Rack PDUs only contain one since as long as they have input power, the outlets will come on.) These power supplies power the switched relays (and also the Network Management Card). If one fails or faults, then you're OK and should work on getting a replacement. If both fail, then the outlet relays will no longer be predictable and controlled. They will likely stay up and in their current state until the PDU loses input power completely and then subsequently, the PDU won't be able to re-energize them on the next boot and then any attached equipment won't turn on.
Long story short, the Rack PDU should be replaced when you have a power supply fault on either #1 or #2.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:08 AM . Last Modified: 2024-03-18 12:04 AM
Hello,
This refers to one of the two internal DC power supplies. Switched Rack PDUs contain a primary and a secondary power supply. (Metered Rack PDUs only contain one since as long as they have input power, the outlets will come on.) These power supplies power the switched relays (and also the Network Management Card). If one fails or faults, then you're OK and should work on getting a replacement. If both fail, then the outlet relays will no longer be predictable and controlled. They will likely stay up and in their current state until the PDU loses input power completely and then subsequently, the PDU won't be able to re-energize them on the next boot and then any attached equipment won't turn on.
Long story short, the Rack PDU should be replaced when you have a power supply fault on either #1 or #2.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.