ACRC502 - Humidifier Commmunication Fault

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • ACRC502 - Humidifier Commmunication Fault
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
serge_onore
serge_onore
Cadet

Posted: ‎2025-01-17 06:49 AM

0 Likes
6
1083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-17 06:49 AM

ACRC502 - Humidifier Commmunication Fault

Hi community!

I have couple ACRC502 units that started exhibiting same problem as in this thread (I cannot post there for some reason):
https://community.se.com/t5/APC-UPS-Data-Center-Enterprise/ACRC502-Humidifier-Commmunication-Fault/t...
In fact, they behave like they are ACRP units (with humidifier and heater) but they are not! So they with through random errors like:

 

Warning Humidifier Communication Fault
Warning Heater 3 Fault
Warning

Return Humidity Sensor Fault

 

Our setup consist of 8 units: 4x ACRP502 and 4x ACRC502, combined in one group. Only ACRC502 will exhibit this problem
All 8 units have same firmware:

* Application Module: acrp v3.9.1
* APC OS (AOS): aos v3.9.2

I could not find specific firmware for ACRC502. It looks like it uses same files as ACRP502. So the question is: how to tell my ACRC units that they don't have humidifier and heaters and stop throwing errors?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
SergioGonzalezQ
Ensign SergioGonzalezQ Ensign
Ensign

Posted: ‎2025-01-30 01:43 AM

0 Likes
0
1014
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-30 01:43 AM

Hello, correct is necessary that a FSR uses the factory mode on the unit and write the following command of "2BW 2" as this removes reheat / humid.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-01-30 03:57 AM

0 Likes
0
999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-30 03:57 AM

Hello,

 

Yes ,the command 02W to set the model number and 03W for serial number. the below needs to be verified as well ,once verified the unit should  correctly work

 

01

Manufacture Name

02

Model Number

03

Serial Number

04

Hardware Revision

05

Manufacture Date

06

Firmware Revision

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-01-28 02:02 AM

0 Likes
0
1030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-28 02:02 AM

Dear,

 

Both ACRP and ACRC units share the same firmware, it is recommended that an SR visit the site and apply the factory commands  to the MB in order to adjust unit model and ensure the R2 SIMM controller is used in these units 

 

Regards,

 

Karim

Reply

Link copied. Please paste this link to share this article on your social media post.

SergioGonzalezQ
Ensign SergioGonzalezQ Ensign
Ensign

Posted: ‎2025-01-30 01:43 AM

0 Likes
0
1015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-30 01:43 AM

Hello, correct is necessary that a FSR uses the factory mode on the unit and write the following command of "2BW 2" as this removes reheat / humid.

Reply

Link copied. Please paste this link to share this article on your social media post.

serge_onore
serge_onore
Cadet

Posted: ‎2025-01-30 02:38 AM

0 Likes
0
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-30 02:38 AM

Hi, it sounds like an easy procedure we can carry ourselves. How I can put unit in factory mode? Should I use serial console connection? Are there special credentials?

Reply

Link copied. Please paste this link to share this article on your social media post.

KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-01-30 03:57 AM

0 Likes
0
1000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-30 03:57 AM

Hello,

 

Yes ,the command 02W to set the model number and 03W for serial number. the below needs to be verified as well ,once verified the unit should  correctly work

 

01

Manufacture Name

02

Model Number

03

Serial Number

04

Hardware Revision

05

Manufacture Date

06

Firmware Revision

Reply

Link copied. Please paste this link to share this article on your social media post.

serge_onore
serge_onore
Cadet

Posted: ‎2025-01-30 05:50 AM

0 Likes
0
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-30 05:50 AM

Can I enter these commands from serial console myself? These units are quite old, out of warranty and out of official support, according to information on product page. So I would be happy if you provide instructions on how to enter factory mode and enter these commands.

Reply

Link copied. Please paste this link to share this article on your social media post.

SergioGonzalezQ
Ensign SergioGonzalezQ Ensign
Ensign

Posted: ‎2025-01-31 01:09 AM

0 Likes
0
855
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-31 01:09 AM

Hello, I would say this is a job from a FSR only, it does require special credentials and experience.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore