Posted: 2025-01-17 06:49 AM
Hi community!
I have couple ACRC502 units that started exhibiting same problem as in this thread (I cannot post there for some reason):
https://community.se.com/t5/APC-UPS-Data-Center-Enterprise/ACRC502-Humidifier-Commmunication-Fault/t...
In fact, they behave like they are ACRP units (with humidifier and heater) but they are not! So they with through random errors like:
Warning | Humidifier Communication Fault |
Warning | Heater 3 Fault |
Warning |
Return Humidity Sensor Fault |
Our setup consist of 8 units: 4x ACRP502 and 4x ACRC502, combined in one group. Only ACRC502 will exhibit this problem
All 8 units have same firmware:
* Application Module: acrp v3.9.1
* APC OS (AOS): aos v3.9.2
I could not find specific firmware for ACRC502. It looks like it uses same files as ACRP502. So the question is: how to tell my ACRC units that they don't have humidifier and heaters and stop throwing errors?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-30 01:43 AM
Hello, correct is necessary that a FSR uses the factory mode on the unit and write the following command of "2BW 2" as this removes reheat / humid.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-30 03:57 AM
Hello,
Yes ,the command 02W to set the model number and 03W for serial number. the below needs to be verified as well ,once verified the unit should correctly work
01 |
Manufacture Name |
02 |
Model Number |
03 |
Serial Number |
04 |
Hardware Revision |
05 |
Manufacture Date |
06 |
Firmware Revision |
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-28 02:02 AM
Dear,
Both ACRP and ACRC units share the same firmware, it is recommended that an SR visit the site and apply the factory commands to the MB in order to adjust unit model and ensure the R2 SIMM controller is used in these units
Regards,
Karim
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-30 01:43 AM
Hello, correct is necessary that a FSR uses the factory mode on the unit and write the following command of "2BW 2" as this removes reheat / humid.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-30 02:38 AM
Hi, it sounds like an easy procedure we can carry ourselves. How I can put unit in factory mode? Should I use serial console connection? Are there special credentials?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-30 03:57 AM
Hello,
Yes ,the command 02W to set the model number and 03W for serial number. the below needs to be verified as well ,once verified the unit should correctly work
01 |
Manufacture Name |
02 |
Model Number |
03 |
Serial Number |
04 |
Hardware Revision |
05 |
Manufacture Date |
06 |
Firmware Revision |
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-30 05:50 AM
Can I enter these commands from serial console myself? These units are quite old, out of warranty and out of official support, according to information on product page. So I would be happy if you provide instructions on how to enter factory mode and enter these commands.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-31 01:09 AM
Hello, I would say this is a job from a FSR only, it does require special credentials and experience.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of