Network Management Card removal and changing IP address
Hi All
I have to remove a Network Management Card from on UPS to another this friday, its a site that has no documentation so i dont know th IP of the card or the passwords for the Netwrok Shutdown agents. When i remove the card will the IP address be stored, if so how can i reset the card to defaults or change the IP address. Once ive done this im going to re-install the Netwrok Shutdonw Agents on all the servers and reconfigure. The card i an ap9617 i have no manuals either, i have quickly searched the site but time is limited as usual, so would be most greatfull if someone could point me in the correct direction.
Thanks in advance
- Labels:
-
Smart-UPS & Symmetra LX | RM
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:00 AM . Last Modified: 2024-03-13 01:55 AM
yes, IP settings will still be intact.
here is some set up information what cables you need, etc -> http://nam-en.apc.com/app/answers/detail/a_id/3061
here is the password reset procedure information -> http://nam-en.apc.com/app/answers/detail/a_id/7879
if you gain access to the NMC by resetting the password, navigate to System->Tools->Reset to defaults and you can reset all the settings. the first article i mentioned here goes through just editing network settings.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:00 AM . Last Modified: 2024-03-13 01:55 AM
yes, IP settings will still be intact.
here is some set up information what cables you need, etc -> http://nam-en.apc.com/app/answers/detail/a_id/3061
here is the password reset procedure information -> http://nam-en.apc.com/app/answers/detail/a_id/7879
if you gain access to the NMC by resetting the password, navigate to System->Tools->Reset to defaults and you can reset all the settings. the first article i mentioned here goes through just editing network settings.