Low runtime remaining on SMART-UPS RT 3000 XL

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Low runtime remaining on SMART-UPS RT 3000 XL
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

0 Likes
7
2995
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

Low runtime remaining on SMART-UPS RT 3000 XL

Hello,

we had a power failure last week on our Smart UPS RT 3000 XL.

We bought it on March 14 2013 (with network card AP9630).

We have a low runtime remaining of 28min 17sec.

Here are the other value given :

UPS Input    
Input Voltage: 219.5 VAC @ 50.0 Hz
 
UPS Output  
Output Voltage: 230.0 VAC @ 50.0 Hz
Load Current: 4.4 Amps
 
Output VA: 33.8 %
Output Watts: 44.6 %
Battery Status  
State of Charge: 100.0 %
Battery Voltage: 218.3 VDC
Num of External Batteries: 0 

I am not sure to change the battery or not ?

Is there an other problem ?

Could someone help me ?

Thanks

Laurent.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

0 Likes
0
2995
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

michael,

Here is the screen shot of the APC :

APC screenshot

Can you see runtime remaining and the "Last Battery Transfer" status ?

Do you think it's normal ?

Thanks.

Laurent.

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

0 Likes
0
2996
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

Hi,

Where are you seeing the error? On the NMC or in PowerChute and if PoewrChute what version? Can you provide the event log/s for each if using PowerChute and what is low battery threshold set for on the NMC?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

0 Likes
0
2996
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

Hi,

I am seeing the error on the nmc web page.

NMC version : hw05_aos640_sumx640_bootmon108

I think (but i am not sure) that low battery duration is 5 minutes.

Please find attached the event log.

Thanks.

Laurent.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

0 Likes
0
2996
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

Laurent,

After looking over your event log, I do not see any low runtime warnings. I see a couple instances where the unit went on battery due to distorted input but that is normal and the unit transferred back off of battery once the input power returned to normal. Overall the unit seems to be in good health. Is there a particular date and time when you saw this? 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

0 Likes
0
2996
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

michael,

Here is the screen shot of the APC :

APC screenshot

Can you see runtime remaining and the "Last Battery Transfer" status ?

Do you think it's normal ?

Thanks.

Laurent.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

0 Likes
0
2996
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

Hi Laurent,

Regarding the "Last Battery Transfer" status, I get the identical message when I pull the plug on the UPS to simulate a real power outtage.

To me, with your UPS loaded to about 40% or so, I think your "run time remaining" indication is reasonable.

Joe

Reply

Link copied. Please paste this link to share this article on your social media post.

mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

0 Likes
0
2996
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

I Agree With Joe. The runtime is right in the expected range for the amount of load you have attached to the unit. If you would like more runtime you can added additional battery packs. 

-Mike

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

0 Likes
0
2996
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

You can buy external batteries to increase the runtime.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore