Symmetra RM 6000 -- Am I on bypass or not?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra RM 6000 -- Am I on bypass or not?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

0 Likes
7
2589
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

Symmetra RM 6000 -- Am I on bypass or not?

I have a (very) remote Symmetra RM 6000 with a single battery installed (don't laugh, it's what the client provisioned.)

The web card was reporting two issues: first it was reporting a faulty battery and second it was (and still is) reporting a system level fan fault. It was also reporting that it was on bypass, ostensibly due to the faulty battery.

Today I got someone to replace the battery, so that problem is gone. The System level fan fault still exists.

After we replaced the battery and took the UPS out of maintenance bypass, there was a system event saying "UPS: No longer in bypass." In the web interface, there is nothing to indicate that the UPS is in bypass and on the Battery System Status page it shows 19 minutes of runtime remaining (I said don't laugh!!) So, I am lead to believe that the UPS is no longer in bypass.

The confusing part is that we have a Nagios SNMP check polling upsBasicStateOutputState which is saying that the UPS is in bypass. According to the MIB, this OID is "an ASCII string containing the 64 flags representing the current state(s) of the UPS." Flag 16 is returning 1. According to the MIB, this means that the UPS is "In Bypass due to Fan Failure."

So which is it? Is the UPS actually in bypass and just not telling me via the web interface, or is the MIB's documentation incorrect?

Thanks for any clarification!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • bypass
  • fan
  • fault
  • mib
  • snmp
  • upsbasicstateoutputstate
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:38 PM . Last Modified: ‎2024-03-06 10:48 PM

0 Likes
0
2592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:38 PM . Last Modified: ‎2024-03-06 10:48 PM

Thanks for your feedback. And you're welcome!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

0 Likes
0
2593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

Hi Sean,

Can you tell me what firmware you have on the Network Management Card (NMC) in the UPS? That way I can know what you're working with. I'd also be interested in any log files you can obtain from it (which will depend on NMC model and firmware version). Instructions here on downloading logs -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156131 .. you can attach them to this post if you're able to obtain them successfully.

Did any on-site person happen to note which LED(s) were illuminated on the UPS display?

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

0 Likes
0
2593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

By the way, the fan is an orderable spare, part number 490-0024B. You can get it from many of the usual places (CDW, etc.) although it is usually not stocked and they have to order it for you. The recommended replacement procedure is to shut down and de-energize the UPS (removing the fan leaves a big opening in the UPS where dangerous voltages are present, and you have to reach in there to get to the fan's plug). It is possible to do it on a live UPS (at your own risk) if you put the UPS into bypass. While nothing should happen if you do it without being in bypass, any glitch can "scare" the Intelligence Module and trigger a fault, which may drop the load.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

0 Likes
0
2593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

Hi Angela,

The NMC is an AP9631 running AOS v6.2.1. I have attached the (sanitized) event log and and the data log. The fan fault happens at 01/18/2016

Unfortunately our on-site person did not note which LEDs were illuminated.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

0 Likes
0
2593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:37 PM . Last Modified: ‎2024-03-06 10:49 PM

Thanks, Angela! 

On 1/20/2016 10:53 AM, Angela said:

I don't see one of those 64 flags that just says "fan fault" so I am guessing maybe it shows this one since its the only option to represent the fault.

That's what I was thinking. Hopefully one of your Symmetra RM folks can confirm for us!

The output of upsBasicOutputStatus is 2, which is 'onLine' so that is encouraging.

I have attached screenshots of the Home page and the Control -> UPS page.

Thanks again for your help!

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:38 PM . Last Modified: ‎2024-03-06 10:49 PM

0 Likes
0
2593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:38 PM . Last Modified: ‎2024-03-06 10:49 PM

Hi Sean,

I confirmed Symmetra RM does not go to bypass when there is a fan fault. Based on all of this, I think flag 16 is just a little misleading and the UPS is online.

As a user with a System Fan Fault, would you prefer to see no flags triggered on the upsBasicOutputState or now that you know, continue to see the flag 16 which is a little misleading since it says in bypass due to fan fault? I think ideally, the answer is to add a new, clarified flag that just says system fan fault to the OID responses but I was just thinking if I ask someone to make adjustments (if it is even possible), what is preferred by a user and what you'd expect ideally as well as with what we have available now to us?

My gut tells me flag 16 is better than no flag at all, especially for those who only monitor via SNMP polling.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:38 PM . Last Modified: ‎2024-03-06 10:48 PM

0 Likes
0
2593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:38 PM . Last Modified: ‎2024-03-06 10:48 PM

Angela,

Agreed, flag 16 is better than no flag at all for our purposes. We can adjust our Nagios check to work with this new information. I also agree that a new, clarified flag would be the ideal solution but in lieu of that, some easily searched documentation in the knowledge base or an amendment to the user manual, or even a note in the MIB itself -- space permitting -- would also be fine.

Of course, asking on the forum evidently works quite well, too 🙂

Have a great day and thanks for all your help!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:38 PM . Last Modified: ‎2024-03-06 10:48 PM

0 Likes
0
2593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:38 PM . Last Modified: ‎2024-03-06 10:48 PM

Thanks for your feedback. And you're welcome!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of