Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

EcoStruxure IT Gateway known issues

What's new in EcoStruxure IT Gateway

Get the latest news, release notes, and other need-to-know information about EcoStruxure IT Gateway

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • Gateway
  • What's new in EcoStruxure IT Gateway
  • What's new in EcoStruxure IT Gateway
  • EcoStruxure IT Gateway known issues
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • EcoStruxure IT forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to What's new in EcoStruxure IT Gateway
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
6125 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

EcoStruxure IT Gateway known issues

Picard EcoStruxureIT
‎2018-11-13 03:44 AM

Last Updated: Sisko JLehr Sisko ‎2025-07-23 11:48 AM

Get a quick overview of EcoStruxure IT Gateway known issues and fixes. If you’re experiencing issues not on this list, or if you have other feedback, please submit a request.

 
  • After updating the Gateway to version 2.0.x, devices with no name can cause the communication between the Gateway and EcoStruxure IT to fail.
    Device discovery counts in the Gateway and IT Expert might not match, and alarm updates might not occur. Sensor measurements are maintained as expected.

    Note: ATS 5G devices with 1.x firmware are known to affect communication.

     

    • Update the ATS 5G device firmware to the latest 3.x version.
    • Make sure the device name is set in NMC device. Log in and go to Configuration > General > Identification. Populate the Name field if it is blank.
    • Delete the device from the Gateway and discover it again.

 

  • We are investigating reports of frequent communication alarms from NMC3 devices. More...

  • The .stage directory may be left behind during a backup. The backup is successful. The error displayed can be disregarded.

  • Gateway restore fails to execute when the locale is set to use Italian, Spanish, or Portuguese as the language. Change the locale to use English to perform the restore.

  • When a proxy server is configured on the Gateway, the files required for software auto update, appliance OS auto update, Device Library update, and firmware update are prevented from downloading.
    Until this issue is addressed in a future release:

    • IT Expert Administrator users can download the latest Gateway software on the Administration > Gateways page and install it manually.
      Note: To update the software on a Gateway appliance, contact support for assistance.

    • Users with appropriate permissions can update device firmware directly on the device.

       

  • When a web browser on the server running the Gateway is left open for an extended time, polling timeouts due to intermittent high CPU and/or memory usage can occur. Close the browser to return system resources to expected levels.

  • The user running the Gateway Linux installer on RHEL or CentOS must have file system privileges set to umask 0022. Otherwise, the installer cannot initialize the database.

  • IT Expert does not receive configuration information for APC devices that were discovered in the Gateway before File Transfer Settings were specified. Make sure the File Transfer Settings in the Gateway are correct for the APC devices you want to discover, and then run the discovery again. Device data will be available in IT Expert after the next polling cycle completes.

  • A security update in Gateway requires that Redfish devices support 2048 bit server certificates. New Redfish discoveries can fail, and previously discovered Redfish devices may be listed as offline. To discover and monitor Redfish devices, install a new certificate on the Redfish device that supports 2048 bit server certificates.

  • Redfish discoveries can fail if SNMP is enabled on the device. Check whether SNMP is enabled on the device you want to discover, disable it, and try your Redfish discovery again.

  • Due to network latency, incomplete data might be displayed for a device, for example, the serial number is missing or sensors are not displayed.
    Check to see if there is a duplicate device in the Gateway device list that displays the correct values; if so, delete the device that displays incomplete information. If no duplicate device exists, c
    heck the network connection for the device, and then delete the device from the Gateway device list and rediscover it.

  • The Unsupported devices and Invalid device credentials lists cannot be modified or deleted from the Gateway user interface.

  • Login to the web page for a Galaxy VS UPS fails when you access it from the device details page in the Gateway. To access the device directly, type its IP address into a browser.
  • When the browser window is maximized, you cannot scroll in the Gateway device list when more than 20 devices are discovered. Reduce the size of the browser window for best results.

  • The SUMX v6.2.0 and v6.2.1 firmware is missing the OID that indicates the number of input phases. This is known to affect the Smart-UPS RT 20000 XL (3 phase UPS) and Symmetra LX 16000 RM (split phase UPS) but may affect others. Upgrade the firmware to either SUMX v6.4.0 or SUMX v6.5.0 to resolve the issue. Get the latest firmware here. For more information see this APC FAQ.
  • TrippLite UPS models SMART100RM1U and SMART750RM1U can show a negative Battery Temperature reading, for example, -13.89 C. Update the firmware on your devices to resolve this issue.
  • NetBotz 200 does not display the temperature correctly when the temperature preference is set to Fahrenheit on the device. You can log in to the NetBotz 200 and change the temperature preference to Celcius in the Administration > General > Preferences option.
  • The serial number does not update in the Gateway when a power module is replaced in a Symmetra PX. Rediscover the Symmetra PX to display the information for new power modules as expected.
    Do not remove the Symmetra from the Devices list.

  • The Gateway installer does not open ports in the firewall to allow access to the web server. You must access the Gateway application from the local host. You can access the application from remote hosts only if you disable the firewall on your computer.
  • Automatically detecting proxy server settings fails in some environments. You can manually configure your proxy server settings. See Installing and setting up EcoStruxure IT

 

Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

Didn't find what you are looking for? Ask our Experts
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of