Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

iTRV Not Closing

Schneider Electric Wiser Forum

Connect with Wiser Smart Home solution experts in the Schneider Electric Wiser forum. Discuss tips on features, updates, installation, and how to get the most out of your Wiser products.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • Schneider Electric Wiser
  • Schneider Electric Wiser Forum
  • iTRV Not Closing
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Alfred_SE
Lt. Commander Alfred_SE Lt. Commander
23
nischaypond
Ensign nischaypond Ensign
4
sesa96364
Lieutenant sesa96364
2
MikeP007
Crewman MikeP007
1
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Schneider Electric Wiser Forum
Fozzie1960
Crewman Fozzie1960
Crewman

Posted: ‎2023-01-24 12:54 AM

0 Likes
7
842
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-24 12:54 AM

iTRV Not Closing

Ever since I installed Wiser I’ve had an issue with iTRVs not closing after the set point has been reached. Drayton diagnosed the issue has incompatible valve heads, i.e non Drayton. They came to this conclusion from photos I sent to them. So I changed two valves, one upstairs and one downstairs. The problem didn’t go  away. Drayton then put the blame on my Wifi connection. I borrowed a wifi tester from work and checked the signal in every room. The worst signal was -60dBm. The signal at the hub was -52dBm. Even with this evidence Drayton still put the blame on my network, which is fully meshed by the way.

 


I’ve reached the point where I’m fed up with resetting valves to make them close and rooms overheating. 

I would like to know if anyone else has experience this issue and have they managed to fix it.

 

Labels
  • Labels:
  • Temperature Control
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
PhilHornby
Lieutenant PhilHornby
Lieutenant

Posted: ‎2023-01-24 06:56 PM . Last Modified: ‎2023-01-24 07:00 PM

0 Likes
0
794
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-24 06:56 PM . Last Modified: ‎2023-01-24 07:00 PM

If the iTRV closes when you twist the cap (blue light) and opens when you twist it the other way (red light), then I think you can say it functioning correctly mechanically. 

 

Assuming that is the case, then you probably have Zigbee comms. issues. Zigbee operates on 2.4GHz and so can suffer interference from Wi-Fi (Wi-Fi always seems to win!). There is no (official) way of displaying which Zigbee channel is in use - and in any case, you can't change it. You could try arbitrarily changing the 2.4GHz channel of your Wi-Fi to see if it improves matters.

 

Otherwise, you will need to purchase a 'Smartplug', which acts as a Zigbee Repeater. (Zigbee Repeaters have to be mains-powered). Again, there is no (official) way of displaying the Zigbee signal levels (which would aid your purchasing decision...)



---------------------
3 Channel Hubᴿ, 13xiTRVs, 8xRoomstats and 2xSmartplug/Repeaters. (UK)
Reply

Link copied. Please paste this link to share this article on your social media post.

turnah
turnah
Cadet

Posted: ‎2023-01-27 12:51 AM

0 Likes
2
762
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-27 12:51 AM

I have the same issue and have had a call open with Drayton for weeks, not getting far with it.

 

My bedroom is currently set at 17 degrees yet is 21 degrees with the radiator hot. So frustrating - there is an issue as it only started happening in the last month or so. It is also happening in other rooms. I have a home assistant setup and can see strong connections on the zigbee mesh.

 

When i reset the TRV it closes completely, then within 30 seconds opens itself again.

 

You're not alone and i'm pretty angry after the amount of money i've spent on this system, it's actually costing me more than my Hive. Support is weak at best.

Reply

Link copied. Please paste this link to share this article on your social media post.

Fozzie1960
Crewman Fozzie1960
Crewman

Posted: ‎2023-01-27 01:19 AM . Last Modified: ‎2023-01-27 01:20 AM

In response to turnah
0 Likes
0
758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-27 01:19 AM . Last Modified: ‎2023-01-27 01:20 AM

Interesting you say that because our kitchen is the room that suffers the most with this phenomenon. Interesting because the iTRV has direct line of sight to the Hub and there’s also a smart plug in the room.

Reply

Link copied. Please paste this link to share this article on your social media post.

david101
Ensign david101
Ensign

Posted: ‎2023-01-27 07:34 AM

0 Likes
0
744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-27 07:34 AM

What SW version are you guys running?  I am on ea64 and I don't have this issue.  I have other issues though like the inaccurate temperature calculations.

Reply

Link copied. Please paste this link to share this article on your social media post.

Fozzie1960
Crewman Fozzie1960
Crewman

Posted: ‎2023-01-27 09:09 AM

0 Likes
0
741
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-27 09:09 AM

ea64

Reply

Link copied. Please paste this link to share this article on your social media post.

turnah
turnah
Cadet

Posted: ‎2023-01-27 09:29 AM

0 Likes
0
734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-27 09:29 AM

Ea64 here too

 

Reply

Link copied. Please paste this link to share this article on your social media post.

PhilHornby
Lieutenant PhilHornby
Lieutenant

Posted: ‎2023-01-27 04:02 PM . Last Modified: ‎2023-01-27 04:03 PM

In response to turnah
0 Likes
0
727
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-27 04:02 PM . Last Modified: ‎2023-01-27 04:03 PM


@turnah wrote:

When I reset the TRV it closes completely, then within 30 seconds opens itself again.

By 'reset', do you mean re-calibrate?

 

If this phenomenon is repeatable, you could try temporarily shutting down Home Assistant and see if it still does it. You could also try with the Hubᴿ temporarily powered-off.

 

(I'm wondering if it's the valve itself that's gone bonkers, or HA telling the Hubᴿ to take some particular action - or possibly even the Hubᴿ itself.  Trying fresh batteries would do no harm either.)

 

I don't know if the iTRVs act autonomously, or if they only follow commands from the Hubᴿ.



---------------------
3 Channel Hubᴿ, 13xiTRVs, 8xRoomstats and 2xSmartplug/Repeaters. (UK)
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc