SCADAPack 6606 Input Output module can not change the Configurable Digital Input/Outputs

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • SCADAPack 6606 Input Output module can not change the Configurable Digital Input/Outputs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
92
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
View All

Recommended Forums

  • EcoStruxure Geo SCADA Expert Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Remote Operations Forum
Start a Topic
Solved
geoffpatton
Captain geoffpatton
Captain

Posted: ‎2025-09-23 07:14 AM . Last Modified: ‎2025-09-23 07:18 AM

0 Likes
3
766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-23 07:14 AM . Last Modified: ‎2025-09-23 07:18 AM

SCADAPack 6606 Input Output module can not change the Configurable Digital Input/Outputs

I am programming for a SCADAPack 474 that will be installed with a 6606 module.

I have added the module in RemoteConnect and for the Configurable Digital Input/Outputs will not let me change them from digital inputs to digital outputs.

The SCADA x70 help implies but does not outright say that you go in RemoteConnect  to Configuration, Physical I/O, Local, select the module and then select the DIO point and change the type. The Type says Digital Input and is greyed out, not selectable.

I can change the Analog Inputs Type just fine from here.

 

This is all offline I do not currently have the SCADAPack to connect to.

 

Labels
  • Labels:
  • RTU
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2025-09-24 01:47 AM

0 Likes
1
749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-24 01:47 AM

The channel direction is set when adding the object association:

AndrewScott_0-1758703542889.png

To change the direction of an existing association, clear the association and then add the association with a different direction.


Andrew Scott, R&D Principal Technologist, AVEVA

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2025-09-24 08:07 AM . Last Modified: ‎2025-11-06 08:42 AM

1 Like
0
733
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-24 08:07 AM . Last Modified: ‎2025-11-06 08:42 AM

Andrew is correct in his response, but I'd just like to add some clarifications for others who might read this thread. The 6606 module was new to me, and I was caught off-guard when trying to replicate Andrew's solution. Two issues arose for me, both worth mentioning:

When you add the 6606 module to the Local Physical I/O you'll be asked if you want to "Manually connect existing objects..." or "Automatically create and connect new objects..."   Select "Automatically create..." as usual. The DIO objects will be created with a Type of Digital Input. You can then select only the DIO channels you want to change to Outputs and click Clear Associations. You can then re-create them to change them to DO type. 

 

As another, somewhat less vital issue, remember that the 6606 module has 16 dedicated DI and 8 dedicated DO points, plus the eight configurable DIO. When wanting to edit DIO1 I accidentally tried editing DI1. Oops! The DIO are separate, further down the list.

 

And as always, don't forget to set the new module's address to 1 or higher, on both the module itself and in RemoteConnect.

 

Joel Weder
Remote Operations Specialist
Schneider Electric

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2025-09-24 01:47 AM

0 Likes
1
750
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-24 01:47 AM

The channel direction is set when adding the object association:

AndrewScott_0-1758703542889.png

To change the direction of an existing association, clear the association and then add the association with a different direction.


Andrew Scott, R&D Principal Technologist, AVEVA
Reply

Link copied. Please paste this link to share this article on your social media post.

geoffpatton
Captain geoffpatton
Captain

Posted: ‎2025-09-24 08:06 AM

In response to AndrewScott
0 Likes
0
736
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-24 08:06 AM

Thanks Andrew. I used the automatically associate when adding the module and that does not ask you to set which they are going to be. It just assumes Input.

Reply

Link copied. Please paste this link to share this article on your social media post.

Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2025-09-24 08:07 AM . Last Modified: ‎2025-11-06 08:42 AM

1 Like
0
734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-24 08:07 AM . Last Modified: ‎2025-11-06 08:42 AM

Andrew is correct in his response, but I'd just like to add some clarifications for others who might read this thread. The 6606 module was new to me, and I was caught off-guard when trying to replicate Andrew's solution. Two issues arose for me, both worth mentioning:

When you add the 6606 module to the Local Physical I/O you'll be asked if you want to "Manually connect existing objects..." or "Automatically create and connect new objects..."   Select "Automatically create..." as usual. The DIO objects will be created with a Type of Digital Input. You can then select only the DIO channels you want to change to Outputs and click Clear Associations. You can then re-create them to change them to DO type. 

 

As another, somewhat less vital issue, remember that the 6606 module has 16 dedicated DI and 8 dedicated DO points, plus the eight configurable DIO. When wanting to edit DIO1 I accidentally tried editing DI1. Oops! The DIO are separate, further down the list.

 

And as always, don't forget to set the new module's address to 1 or higher, on both the module itself and in RemoteConnect.

 

Joel Weder
Remote Operations Specialist
Schneider Electric
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore