Question about DNP3 Configuration in Scadapack474

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • Question about DNP3 Configuration in Scadapack474
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
75
BevanWeiss
Spock BevanWeiss
20
sbeadle
Kirk sbeadle Kirk
17
MartinChartrand
Captain MartinChartrand Captain
15
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Remote Operations Forum
Solved
Scadapack474
Scadapack474
Cadet

Posted: ‎2025-05-05 11:54 AM

0 Likes
1
55
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-05 11:54 AM

Question about DNP3 Configuration in Scadapack474

Hi, I am working on a project with Scadapack474 and VTScada where I am using DNP3, there is an option in remoteconnect under the basic tab in the object editor which says periodic event generation. If I enable this option for every 10 seconds will it generate timestamped events every 10 seconds even if there isn't a value deviation? Also is there a way to check if events are being stored in the buffer? I do see a message saying "An Event buffer on the DNP3 Outstation has overflowed" but I'd like to see if new events are being generated. I want to troubleshoot this because I don't see events generated when the master (VTScada) loses connection with the slave (Scadapack474) backfilling in the historical data viewer. I'm testing analog objects configured with a static point class 30v5 and a non-local and non-static event class (some are 1, some 2, some 3). On VTScada im addressing the analogs like so: 30/0/1:NS for DNP3 point AI,1 etc.

Labels
  • Labels:
  • DNP3
  • RTU
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Next Topic

Accepted Solutions
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2025-05-06 09:27 PM

0 Likes
0
26
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-06 09:27 PM

Periodic Event Generation is exactly that.  It will put an Event into the Event Buffer.

That you're seeing "An Event Buffer on the DNP3 Outstation has overflowed" sounds like a problem you'll want to fix though, it's likely an issue with your VTScada configuration where it's not actually retrieving the Events from the buffer successfully.

Are you testing this on a bench, or do you have it via Radio / Cellular Modem etc?

 

The other possibility is that you have the Event Buffer size set overly low.  I'd generally recommend having this high, like 40,000... newer models accept 100,000...

However... keep in mind that if you've got a huge number of events to transfer, this will bog down your network during the transfer.  And can cause problems if you have things like Max TX Keying Time enabled on certain radios (since the TX will be long.. and the radio might just disconnect before it's finished, aborting the transfer).


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2025-05-06 09:27 PM

0 Likes
0
27
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-06 09:27 PM

Periodic Event Generation is exactly that.  It will put an Event into the Event Buffer.

That you're seeing "An Event Buffer on the DNP3 Outstation has overflowed" sounds like a problem you'll want to fix though, it's likely an issue with your VTScada configuration where it's not actually retrieving the Events from the buffer successfully.

Are you testing this on a bench, or do you have it via Radio / Cellular Modem etc?

 

The other possibility is that you have the Event Buffer size set overly low.  I'd generally recommend having this high, like 40,000... newer models accept 100,000...

However... keep in mind that if you've got a huge number of events to transfer, this will bog down your network during the transfer.  And can cause problems if you have things like Max TX Keying Time enabled on certain radios (since the TX will be long.. and the radio might just disconnect before it's finished, aborting the transfer).


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of